    daikin AF fault



    hi guy's

    a customer keeps getting this on a few of in ceiling ducted units

    any idea's

    cheers

    richard
    Attached Images Attached Images



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    20

    Re: daikin AF fault

    if its a daikin sky air f series iam sure AF is drain level means the same as A3 drip pan,pump,float switch,overflow ect ect
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Mar 2005
    Location
    Lanzarote
    Age
    41
    Posts
    372
    Rep Power
    20

    Re: daikin AF fault

    I think your right superswill. We had a problem a few years ago with a Daikin ducted system where the level sensor had got stuck. I´m 99% sure that gave a AF fault.

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: daikin AF fault

    G'day Richard

    AF= Malfunction of humidifier system

    According to the info that I have.
    (You probably knew that anyway)

    As for the cause.I have no ideas.

    Regards.

  5. #5
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: daikin AF fault

    Im sure its a drain problem.Could be a few things such as water flowing back or clogged drian.

  6. #6
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Smile Re: daikin AF fault

    AF means that at thermostat off/condenstate pump off the float switch has made, so good chance that the drain is installed over its max limit and when the condensate pump goes off the water runs back in to the unit. Worth while checking that if the drain upstand is at its max height the pipe size should be reduced to 3/4 from 1" 1/4

    A3 means the the float switch has made whilst the condensate pump is running. probably blocked drain! get the drip pan out and clean it!

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  3. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  4. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM
  5. Daikin Indoor Unit
    By ebo in forum Air Conditioning
    Replies: 10
    Last Post: 15-03-2006, 03:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •