glass display case compressor on, off, on, off......
I am working on an old refrigerated glass case, when I powered it up it imeadiately kicked the breaker in the breaker box, arced and smoked. I replaced the condenser fan motor, now the unit will power up and the compressor will run for a 20 to 30 seconds then shut down, then on again and shut down. All other components seem to be working properly, and the sight glass seems to read sufficient refrigerant. Thanks for any help.
Last edited by fix_it_man74; 27-07-2006 at 04:27 AM.
-
27-07-2006, 06:11 AM #2
Re: I may be spittin in the wind, but...
Hi, It's may be protected by high/low pressure protector, suggest you check the high/low pressure.
-
27-07-2006, 06:34 AM #3
Re: I may be spittin in the wind, but...
hy ! you can check also the relay start of the compressor ar the capacitor..
-
27-07-2006, 07:07 PM #4
Re: glass display case compressor on, off, on, off......
Originally Posted by fix_it_man74
Hi fix it
the compressor bimetal klixon for over current, could it possibly be cutting out
Using a clamp meter I would check the compressor run amps
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes: