    Jan 2005
    South Wales
    52
    11
    compressor oil charging?
    Hi all,
    Would anyone inform me of the correct way to top up the oil in screw compressors? I`ve talked to a few people on this subject and the procedure differs slightly depending who I talk to! Any help on this matter would be great!
    Jun 2001
    N.Ireland
    1,630
    Re: compressor oil charging?
    Quote Originally Posted by THERMOACC
    Hi all,
    Hi Thermoacc
    different compressors different methods.
    I have two methods.
    1/ shut off compressor from system remove the refrigerant, vac compressor out and suck ther new oil into the oil tank.
    2/ connect an electric oil pump to a charging point on the oil tank, open the valve and pump the oil in.
    Hope this helps.
    Kind Regards Andy
    Mar 2006
    Merate (LC) - Italy
    2,549
    Get a used small 5 liters liquid receiver. Connect two capillary pipes with in-line shutoff valves to inlet and outlet. Install a cap to the dafety valve threaded connection.
    Pour oil through the said connection, top it up and close the cap, then vacuum the liquid receiver.
    Connect the inlet capillary to the high pressure of compressor, and the outlet capillary to the low pressure.
    Open the high side valve completely, and slowly open the low side valve until you hear the oil going through.
    Close the valves when happy.
    Disconnect the capillary, beware of the oil spray.
    Feb 2006
    The oil in most screws is highly viscous (thick). The method for getting it in will vary from make to make.
    For instance in an Hitachi the easiest method is to remove the large pressure relief Vv on the discharge housing and simply pour it in (please pump out the gas first). Avoid keeping the oil exposed to air for too long as it is very hygroscopic (absorbs moisture). The compressor should be thoroughly evacuated afterwards.
    Another method is to put the oil is a small liquid receiver and purge it in using OFN at a higher pressure than the system standing pressure, but if you use this method the receiver should be pressure tested appropriately above the purge pressure and use of a sightglass in the line is vital to prevent ANY nitrogen entering the compressor. If this does happen the compressor will require to be vacced out.
    Warming the oil to reduce the viscosity also helps greatly.
    Jan 2006
    Valrico, Florida
    509
    Quote Originally Posted by THERMOACC View Post
    Hi all,
    For Nh3, I usually pump down the compressor, and add it straight into the oil separator with an electric pump.
  1. Refrigerant charging weighing scale
    By malik55 in forum Tools and Calculators
    Last Post: 06-11-2006, 11:14 PM
  2. Charging formula
    By zimbo in forum Trouble Shooting
    Last Post: 28-12-2005, 10:11 PM
  3. Car a/c charging chart
    By chilly in forum Transport
    Last Post: 07-09-2005, 08:18 AM
  4. System charging
    By Dylan in forum Fundamentals
    Last Post: 17-12-2004, 10:37 PM
  5. Charging Adaptor for BMW
    By Abe in forum Air Conditioning
    Last Post: 11-09-2002, 08:31 PM