York chiller system trouble shoot
hi guys, can anyone help me to solve the the problem i m facing.i m working out a york chiller system model:yca 112. the system trip when compressor cut in.LED display show MP/HPCO. as what i found out is the liquid line solenoid valves is off. but after measure from the PCB board, there is no command from the system. i had really a hard time figuring out this incident.hope someone out there will assist me .thanks you
-
30-07-2006, 09:17 PM #2
Re: York chiller system trouble shoot
some chillers have pump down start so the fact that the solenoid valve is n't energized may well be normal. I would check the motor protection module inside the compressor terminal box, i have had several fail due to dry joints on the pcb.
-
31-07-2006, 10:30 AM #3
Re: York chiller system trouble shoot
take off power from compressor and start unit if system is not triping your compressor is faulty
-
17-01-2007, 03:50 PM #4
Re: York chiller system trouble shoot
On Alot Of York Systems The Liquid Line Solenoid Closes And The Comp. Shuts Down On Low Suction, So Have No Power To The Valve Is Normal
-
06-03-2007, 06:54 PM #5
Re: York chiller system trouble shoot
try the current transformer, if it starts and the ct recognises there is no current drawn it may shut the compressor out.
start the compressor and put you amp probe and compare that with what the ct is saying
Similar Threads
-
York Chiller
By HVACGod in forum CommercialReplies: 12Last Post: 11-09-2010, 06:05 AM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
York Chiller
By RubenJLL in forum Trouble ShootingReplies: 20Last Post: 18-04-2008, 04:08 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM