    hi guys, can anyone help me to solve the the problem i m facing.i m working out a york chiller system model:yca 112. the system trip when compressor cut in.LED display show MP/HPCO. as what i found out is the liquid line solenoid valves is off. but after measure from the PCB board, there is no command from the system. i had really a hard time figuring out this incident.hope someone out there will assist me .thanks you



  2. #2
    Join Date
    Jul 2006
    Location
    uk
    Age
    44
    Posts
    49
    Rep Power
    0

    Re: York chiller system trouble shoot

    some chillers have pump down start so the fact that the solenoid valve is n't energized may well be normal. I would check the motor protection module inside the compressor terminal box, i have had several fail due to dry joints on the pcb.

  3. #3
    Join Date
    Jul 2006
    Location
    Australia
    Age
    52
    Posts
    28
    Rep Power
    0

    Re: York chiller system trouble shoot

    take off power from compressor and start unit if system is not triping your compressor is faulty

  4. #4
    Join Date
    Jan 2007
    Location
    USA
    Posts
    37
    Rep Power
    0

    Re: York chiller system trouble shoot

    On Alot Of York Systems The Liquid Line Solenoid Closes And The Comp. Shuts Down On Low Suction, So Have No Power To The Valve Is Normal

  5. #5
    Join Date
    Feb 2007
    Location
    united kingdom
    Age
    56
    Posts
    6
    Rep Power
    0

    Re: York chiller system trouble shoot

    try the current transformer, if it starts and the ct recognises there is no current drawn it may shut the compressor out.
    start the compressor and put you amp probe and compare that with what the ct is saying

Similar Threads

  1. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. York Chiller
    By RubenJLL in forum Trouble Shooting
    Replies: 20
    Last Post: 18-04-2008, 04:08 PM
  4. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 23-03-2004, 11:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •