    Mitsubishi Heavy Industries HELP



    First split I've ever put in, but i'm a bit confused, The felx cable fromt he indoor unit, I take it this is a the power cord and it needs a 3 core + earth to link the two together ???? Not to clear in the instructions



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsubishi Heavy Industries HELP

    WHOA!, STOP!

    Just read the installation instructions carefully.

    Normally, but not absolute, power to outdoor unit, link power from outdoor to indoor unit; separate cable with control connection between indoor and outdoor unit.

    If you can give details of the model then we might be able to provide more detailed information.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2005
    Location
    England
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi Heavy Industries HELP

    its a srk 28,

  4. #4
    Join Date
    Dec 2005
    Location
    England
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi Heavy Industries HELP

    It has a flex hard wired in and there is a 4 point terminal block on both the indoor and outdoor units

  5. #5
    Join Date
    Jun 2006
    Location
    Ireland(ROI)
    Age
    44
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi Heavy Industries HELP

    A lot of the newer smaller splits have the mains into the indoor and then to the outdoor.
    If there is a flex coming out of the indoor unit, this would lead me to believe that this is the case here.

  6. #6
    Join Date
    Sep 2005
    Location
    South West
    Age
    50
    Posts
    129
    Rep Power
    19

    Re: Mitsubishi Heavy Industries HELP

    Quote Originally Posted by Bakerbj
    First split I've ever put in, but i'm a bit confused, The felx cable fromt he indoor unit, I take it this is a the power cord and it needs a 3 core + earth to link the two together ???? Not to clear in the instructions
    Three core goes to spur/plug (yes i know it shouldn't really go to a plug but i am sure it will!)

    Connect 4 core cable which you will supply your self from the indoor unit to the outdoor compressor. They are number 1,2,3,4 in both units.

    Hope this helps.

  7. #7
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Mitsubishi Heavy Industries HELP

    Which SRK28 is it ZD (Inverter)?

    Are you saying...
    Mains feed into the Inside Unit from power supply,
    Then Live, Neutral, Control and earth to the Outside unit?
    Thats opposite to the Daikin method?

    So surely both cables would need to be at least 2.5mm. Low power unit fed first? Full load runs via the inside unit?

    Still needs local emergency isolation close to the outside unit (20a Disconnector switch) Breaking only Live an Neutral? (Not earth & control wire) of the linking cable.

  8. #8
    Join Date
    Dec 2005
    Location
    England
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi Heavy Industries HELP

    thanks for that, didn't want to make a tit of my self o nthe first job. Also in the instructions is says to lag both the liquid and gas pipes in the same insulation ? shouldnt they be seperatly lagged ?
    Last edited by Bakerbj; 25-07-2006 at 12:03 AM.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi Heavy Industries HELP

    Quote Originally Posted by mick2me
    Are you saying...
    Mains feed into the Inside Unit from power supply,
    Then Live, Neutral, Control and earth to the Outside unit?
    Thats opposite to the Daikin method?

    So surely both cables would need to be at least 2.5mm. Low power unit fed first? Full load runs via the inside unit?

    Still needs local emergency isolation close to the outside unit (20a Disconnector switch) Breaking only Live an Neutral? (Not earth & control wire) of the linking cable.
    On some small wall units, Fujitsu, Mitsubishi, Hitachi & Daikool among others, all come with a power cord attached to the indoor unit for connection into a local supply. The interconnecting cable then supplies power/reversing valve/cond fan to the outdoor. As they run at low amps, (4/5A) 1.5mm cable is normally sufficient as this is rated for 19A.

    Local isolation at the outdoor is necessary to comply with BS7671.

  10. #10
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Mitsubishi Heavy Industries HELP

    Quote Originally Posted by frank
    On some small wall units, Fujitsu, Mitsubishi, Hitachi & Daikool among others, all come with a power cord attached to the indoor unit for connection into a local supply. The interconnecting cable then supplies power/reversing valve/cond fan to the outdoor. As they run at low amps, (4/5A) 1.5mm cable is normally sufficient as this is rated for 19A.

    Local isolation at the outdoor is necessary to comply with BS7671.
    Thanks Frank

    If I ever get this Daikin installed, A Mitsubishi SRK**ZD may be my purchase, for upstairs.

  11. #11
    Join Date
    Dec 2005
    Location
    England
    Posts
    28
    Rep Power
    0

    Re: Mitsubishi Heavy Industries HELP

    Installed it and work a treat, the cable is the power cable. H*P said you can just stick a 13a plug on the end, but i wired into a fused spur

Similar Threads

  1. Mitsubishi problem
    By marc5180 in forum Trouble Shooting
    Replies: 15
    Last Post: 17-01-2007, 10:06 PM
  2. Mitsubishi heavy industrial A/C.
    By Langer in forum Air Conditioning
    Replies: 10
    Last Post: 14-08-2006, 11:31 AM
  3. MITSUBISHI Heavy Industries
    By coolit24 in forum Air Conditioning
    Replies: 8
    Last Post: 06-03-2006, 08:46 AM
  4. Mitsu Heavy Industry
    By bobjob in forum Air Conditioning
    Replies: 1
    Last Post: 14-07-2005, 11:00 PM
  5. Mitsubishi Heavy Industry
    By Abe in forum Air Conditioning
    Replies: 7
    Last Post: 09-03-2005, 08:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •