I was wondering if there is any damage to be caused by leaving an oversized capacitor on a fan or compressor after an emergency repair. Like a 45 /7.5 when the original was a 35/5. .
-
24-07-2006, 03:50 AM #2
Re: Split Capacitors on Resi AC
Originally Posted by crisrsLast edited by wambat; 24-07-2006 at 04:13 AM.
-
27-07-2006, 01:01 AM #3
Re: Split Capacitors on Resi AC
I can say from my experience with my system shutting down during hot outdoor temperatures, that the larger sized capacitor will cause the fan motor to run hotter and consume more power. You can expect the compressor to do likewise. Just as you're describing, I made an "emergency repair" and forgot about the excess sized capacitor. It took a long time to figure out the cause of intermittent shutting down.
My recommendation is to locate the correct part that has been engineered for your application.