    Re: lowering freezer temp ?

    Hi Knightly

    Probably not enough head height in the room, but when building rack/trolley freezers, we would fit a false ceiling.
    This is basically a set of fridge panels running horizontal in frount of the cooler (like an extension of the drip tray). The cold air off the cooler is blown over the false ceiling (the racks are wheeled under the false ceiling) the air then returns through the racks bck to the cooler (small 1 foot sections of plastic curtain are hung under the false ceiling to stop the air taking a short cut back to the cooler above the racks).

    This set up will make a big difference to your freezing time (provided that no short cuts are left for the air, ie gaps around and above the racks, or racks left out of the rows).

    Hope this helps

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: lowering freezer temp ?

    Quote Originally Posted by Andy
    Hi Knightly

    Probably not enough head height in the room, but when building rack/trolley freezers, we would fit a false ceiling.
    This is basically a set of fridge panels running horizontal in frount of the cooler (like an extension of the drip tray). The cold air off the cooler is blown over the false ceiling (the racks are wheeled under the false ceiling) the air then returns through the racks bck to the cooler (small 1 foot sections of plastic curtain are hung under the false ceiling to stop the air taking a short cut back to the cooler above the racks).

    This set up will make a big difference to your freezing time (provided that no short cuts are left for the air, ie gaps around and above the racks, or racks left out of the rows).

    Hope this helps

    Kind Regards Andy
    Please see attached, I hope it comes out alrights.

    Air flow is from left to right, from the cooler to above the false ceiling (the cooler shown here is a special with the fans on the return air, most commercial coolers have the fans on the air off).


    Kind Regards Andy
    Attached Images Attached Images
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Lo Temp Freezer Construction
    By Dan McMahon in forum Technical Discussions
    Replies: 14
    Last Post: 06-01-2010, 12:15 AM
  3. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 11:56 AM
  4. Optimum temp in 5 door freezer
    By Joe Painting in forum Commercial
    Replies: 3
    Last Post: 03-06-2006, 07:20 AM
  5. Multiplex For Low Temp and Medium Temp
    By allanbaker in forum Technical Discussions
    Replies: 0
    Last Post: 28-11-2002, 10:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •