    Exclamation Honeywell coolmaster recharge



    Hi. I have two Honeywell Coolmaster air con units which had pipe damage. I have brazed up the pipes and they are ready to be recharged. They are set to run on R22. Any tips on how to go about it. (I have had them on a deep vacuum for 90 minutes each)



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    Charge them to superheat and/or subcooling.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    Thanks for the reply, I have charged the one with the specified weight through the single connector. It took the charge but is not chilling down, any clues?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    Depends on has happened to the unit when it was running with holes in the pipes; could be rotten oil and gunge stuck somewhere in the system.

    Might be worthwhile degassing it and fitting another pressure tapping so that you can see what's happening.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    As I mainly do cars can I just check I re-charged correctly. The BOC R22 gas bottle was valve up. I have also now charged the second unit and that is not chilling down either. The compressor is running and the low pressure line is getting hot on both units. Now I am really confused. Cheers. Mike

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    Sorry, should have asked earlier as I don't know these units....

    Are the heat pumps? if they are then it could be a problem with the reversing valves or controls.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    They are not heat pumps they have heating elements in the blower housing to provide heat.

  8. #8
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Honeywell coolmaster recharge

    This could be a number of things. a suction pressure and selection of air on/off temps would help for starters.
    Takes a licking, keeps on ticking.

  9. #9
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Honeywell coolmaster recharge

    Quote Originally Posted by autochill
    They are not heat pumps they have heating elements in the blower housing to provide heat.
    Pressures and temperatures

    Suction Pressure (discharge if you can) converted to saturated temperature.

    Suction temperature at the indoor unit

    liquid temp off the condenser

    and compressor discharge pipe temp

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  10. #10
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    When the machine is not running the gauge reads 3.5 bar on turning the machine on it goes into vacuum. Not sure if this gives you any better ideas.

  11. #11
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Honeywell coolmaster recharge

    Sure the leak was fixed ,also check for any restrictions What was the charge weight that u say was put in?

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    Auto, which pipes were damaged and required brazing ?

    The fact that the compressor is pulling a vacuum could be a good thing, at least you know that they are pumping!!!

    The suction line is getting warm because there isn't any cooling gas running through it; you have a blockage somewhere or a valve closed.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  13. #13
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    The high pressure line from the condensor was damaged. I was starting to suspect that the info. given by the owner may be a bit suspect. He claims they have been working but ( as they all seem to say) it just needs re-gasing. The charge put in one was 60g in the other 50g. I think he may have moved them and then not reconnected them up properly. Which valves may be closed do you think as I can't see any?

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    I'm sorry I thought you were talking about air conditioning units but judging by the charge that you have put in, 60g and 50g, they must be something an awful lot smaller.

    Even a domestic fridge will take more than that.

    What exactly are these units please Auto.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    They are Hoeywell HCL-140E free standing aircon units with an exterior condensor. Sorry just checked what I typed it was 500g on one and 600g on the other not 50 and 60.

  16. #16
    Join Date
    Jul 2006
    Location
    Northern Ireland
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    Hi looks like you are short on gas....whats the high side (discharge) pressure like? Is the pipe run overly long if so the you'll need more refrigerant.

  17. #17
    Join Date
    Jul 2006
    Location
    uk
    Posts
    8
    Rep Power
    0

    Re: Honeywell coolmaster recharge

    Thanks for your help. the problem turned out to be that the units had been used in a brick works and because of the damaged pipes the evaporater was blocked with dust after flushing and re-charging they both worked fine. Cheers. Auto.

  18. #18
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Honeywell coolmaster recharge

    Hi Auto,

    Thanks for coming back with your results, it's always good to hear that a problem has been resolved and we appreciate your good manners in letting us know.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. honeywell handbook
    By Lc_shi in forum Refrigeration Books
    Replies: 23
    Last Post: 24-05-2010, 08:18 PM
  2. the best way to recharge a VRV/VRF
    By marc5180 in forum Technical Discussions
    Replies: 19
    Last Post: 27-08-2007, 10:59 PM
  3. Coolmaster CU200, leaking
    By Tycho in forum Domestic
    Replies: 18
    Last Post: 14-11-2006, 10:00 PM
  4. Honeywell Blue Book
    By HVACGod in forum Technical Discussions
    Replies: 0
    Last Post: 13-05-2006, 03:07 AM
  5. Honeywell Elm Tuscan e pack controller
    By Mark in forum Supermarket Refrigeration
    Replies: 7
    Last Post: 19-10-2004, 03:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •