    Pipe Contamination in NH3 Systems



    This morning one of my clients asked me to look into a problem they have found in the ammonia piping. They were noticing a small ammonia smell in a freezer.

    Upon inspection they found this flange that was leaking. When they took the flange apart to replace the gasket and inspect the flange, they found the stuff you see in the picture.

    I'm still looking into the details for location of this flange, etc. I will post more information as it becomes available.

    Has anyone seen anything like this before? This is a new situation I have not seen before.
    Attached Images Attached Images



  2. #2
    Join Date
    Jul 2005
    Location
    UK
    Posts
    60
    Rep Power
    19

    Re: Pipe Contamination in NH3 Systems

    Copper Oxide?

    I know, it's ammonia.....

    Why not get it analised. If you've got it in one plece it's probably throughout the system.
    .
    Sodd's the name...... Law's the game.
    Established 1791 - still going strong.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    Greetings.

    I have asked the client if they had it analyzed, but have not had a reply as of yet.

    From the appearance in the picture, and since it was found at a leaking joint, I'm wondering if it might be due to minerals from the air borne water entering into the pipe during normal operation.

    The system runs in a vaccum during normal operation, so moisture could be drawn in during this time. The water will be absorbed by the ammonia, but the scale could be deposited in the piping at that point.

    During defrost, the pressure would be higher, so the leak would travel in the opposite direction and release ammonia.

    This is going to be interesting...

  4. #4
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Pipe Contamination in NH3 Systems

    Ive seen something similar, but in a bubbler tube and drain on a purger, it was calcium and mineral build up from the water and ammonia mixing in the bubbler.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    I've seen that before too, but it's been a long time ago. I seem to remember the scale was sort of brown like shown in the picture.

    Is that what you remember seeing also?

    Thanks for the input.

  6. #6
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Pipe Contamination in NH3 Systems

    It looked exactly like the picture, its fresh in my memory due to it happening 2 months ago.

    How deep of vacum are they running?

    The facility were this happened was ruuninning approx. 10 inchs.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    I believe this location is only running about 2-3 inches of vacuum, depending on what is going on.

    Over a long period of time I suppose something like this could occur. A vacuum is a vacuum after all.

  8. #8
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    51
    Posts
    135
    Rep Power
    19

    Re: Pipe Contamination in NH3 Systems

    Looking at it, no idea what it is, but if it is water scale the it hasn't come from the air, airborne moisture contains nothing but air and water. Scale would have to be from a water leak - mains water or cooling loop. Best bet is to get it analysed, not sure if you have anyone in mind as it's not the usual sort of thing for a refrigerant lab. The techinque of choice for thsi would be XRF (X-ray fluorescence), which is common in metallurgical analysis, but a good contract lab should tell you that!
    It's a lovely day to pump some gas

  9. #9
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: Pipe Contamination in NH3 Systems

    Us Iceman

    What is the product they are freezing? Could it be something from that? Is the build up solid or flakey when touched?

    Refteach

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    The picture is all I have to go on right now. This is for a cold storage facility, so nothing fancy.

    The contamination in the pipe was described to me as similar to calcium scale on evaporative condensers, or in water pipes.

    I'm still waiting on some answers to earlier questions I sent to the client.

    Quite interesting, huh?

    BTW, why aren't you working?

  11. #11
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: Pipe Contamination in NH3 Systems

    It was close to quiting time.

    Try some lime away on a small sample to see if it will disolve? If it does then it points to calcium build up which is unusual to say the least, any idea on H2O content in the system?

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    Quote Originally Posted by refteach
    ...any idea on H2O content in the system?
    Not at this time. A lot of details and answers are still unknown.

    Let me guess, now it's almost lunch time?

  13. #13
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23

    Re: Pipe Contamination in NH3 Systems

    Quote Originally Posted by US Iceman
    From the appearance in the picture, and since it was found at a leaking joint, I'm wondering if it might be due to minerals from the air borne water entering into the pipe during normal operation.

    The system runs in a vaccum during normal operation, so moisture could be drawn in during this time. The water will be absorbed by the ammonia, but the scale could be deposited in the piping at that point.
    If it is water, it looks about right to me. If it is "chalky" in consistency, I have seen similar from a leaking condenser tube, hanging as a stalactite from the offending tube. The brown colour could easily be absorbed from rust in the pipe if water was present.

    Steve

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Pipe Contamination in NH3 Systems

    What I don't know is if this evaporator is water defrost? If so, I think we could make a good case for the junk being scale.

    But, I have to agree with Johnny Rod. Testing tells the true story, and I really hate to guess at things.

    Still waiting on the client for some answer to early questions.

    I'll keep you guys posted on future developments. Thanks to all for participating. I appreciate you taking the time to contribute.

  15. #15
    Join Date
    Dec 2007
    Location
    Nebraska
    Age
    76
    Posts
    25
    Rep Power
    0

    Re: Pipe Contamination in NH3 Systems

    Ahhh, that familier blue. the gasket was moist, probably laying around soaking up moisture.
    It could also be from the flange itself.
    A little "never sieze" goes a long way to stop this.
    It does have mass.

Similar Threads

  1. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 04:10 PM
  2. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •