    Went out to a 7Kw Fujitsu Cassette Air Conditioning Heat Pump today.

    All I heard was a hum, come from the compresor...........and then it stopped.

    It did not shudder or shake. It just hummed for around 15secs or so...........and then stopped humming.

    Condenser fan continued to run.

    I told customer he needs a new compressor. But, I am wary......He told me it never worked right in cooling mode since it was installed two years ago.

    It worked ok in heating...............apparently

    What if I change the compressor and it blows , because of a fault with say the three way valve..........

    Maybe the install was bad.........too much R410 put in......

    Im not sure............

    Would it be better just to fit a new Outdoor unit?
    Is it the compressor?

    What other checks should I have carried out.

    I am not familiar with Fujitsu on troubleshooting.......

    Any help appreciated

    Mode No AOY25UNAKL
    Serial No T 000348

    R410
    7Kw



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fujitsu

    I'd go with a new unit.

    If you have to change a compressor then you should also do the reversing valve. One may have killed the other but you don't know which one did it first.

    Tell the customer that with the material and labour costs plus the lack of warranty that new is cheaper/better in the long run.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Fujitsu

    If it is a current condensing unit a unit will work out a few hundred pound more fitted! I had a 14kw Fujitsu I changed a compressor on and the bugger went down on both blocked filter driers, I spent hours with it, when I priced out a complete outdoor unit which would of saved me a load of hassle it was only £250 more than a compressor and contactor and bear in mind it had a new rev valve, 2 fan motors, circuit board.........I was horrified.

  4. #4
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Re: Fujitsu

    Well 15 sec is enought to check 4V by thermometer.Also the gauges would tell something.If it is 4V than suction pressure would be higher then normal.But you know all that.

    Renato

  5. #5
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Fujitsu

    G'day Abe.

    Have you checked the run capacitor?

    Does it have a soft start?

    Have had a similar problem where a unit under warranty lost 2 compressors over a 2 year period. Turned out to be a partial restriction of the capillary assembly.

    Symptoms was a unit that appeared to work although not quite properly with a slightly lower than normal suction pressure.Compressor would occasionly fail on thermal due to lack of compressor cooling.

    Regards.

  6. #6
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Fujitsu

    Sounds like it is siezed, what was the current draw?
    it is faster and easier to replace to cond unit rather than the pot. its your choice, but i know what i would do.
    Takes a licking, keeps on ticking.

  7. #7
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Fujitsu

    Ive quoted a new Unit.......895.00 List

    Compressor alone is around 300.00 mark

    Does not make sense to fit compressor in case there are other underlying probs with say, restriction in cap tube, three way valve not closing tight, etc.

    I dont want sleepless nights and going back to and fro to the unit.

    This way Ill fit a new outdoor unit, and use the old one , convert it to use in a cold room or a air handling situation.

    The blanket wrapped around the compressor. It only served to make the compressor baking hot.

    Is it acceptable practice to remove it completely....

    Ok, it will make the sound level increase, but what other purpose does it serve???

  8. #8
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Fujitsu

    Quote Originally Posted by Renato RR
    Well 15 sec is enought to check 4V by thermometer.Also the gauges would tell something.If it is 4V than suction pressure would be higher then normal.But you know all that.

    Renato

    Renato

    Can you elaborate please.

    15 secs is enough to check 4v by thermometer , of what?

    Gauges dont move, compressor does not start, it only hums

    Much appreciated

    Thx

  9. #9
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Post Re: Fujitsu

    Ok.I miss understend you.So compressor doesnt start at all.Then did you check resistance betwen C,S and R.Firs remove start relay and measure with unimer C-S,S-R,C-R.But condenser fan shouldnt start if compressor doesnt run.

    Seams easy but then again it is problem to come again to machine becose you can charge that.

    Renato

  10. #10
    Join Date
    May 2004
    Location
    England
    Age
    53
    Posts
    111
    Rep Power
    20

    Re: Fujitsu

    Quote Originally Posted by Abe
    The blanket wrapped around the compressor. It only served to make the compressor baking hot.

    Is it acceptable practice to remove it completely....

    Ok, it will make the sound level increase, but what other purpose does it serve???
    i don't know about Fujitsu, but Hitachi always said to leave it in place as it served to stop you burning your arm when you stuck it in, they used to run red hot.

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2007, 09:06 PM
  3. Fujitsu Password
    By sigorst in forum Air Conditioning
    Replies: 0
    Last Post: 02-01-2006, 09:56 PM
  4. Fujitsu hp's icing
    By rbartlett in forum Air Conditioning
    Replies: 8
    Last Post: 08-01-2005, 09:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •