    Selection Opinions.



    i'm seeking opinions on what should just be straight forward budget pricing, but the more i look at it, the problems it's throwing up.

    The air is approx 25m long, by 8.5m deep. O/all height is 2.7m ground floor and 2.8 for the mezz floor. (mezz is basically same size)

    The front is all glazed, no shade or blinds etc and faces SW.

    Space for plant is very limited on the roof, and i need fresh air at 12 l/s for 200 people.

    Having done several methods of calc, they are all coming out bigger than the last, mainly solar from the windows and gain from the supply air.

    I want to use outdoor ambient of 33c, maybe 35c to be safe.

    Anyone got any feeling for total UK duty?



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Selection Opinions.

    The glass is an obvious way of solving this.

    Remove a pane at a time block out with plywood and replace with a window rattler. This will have a duel effect as it removes heat with the rattler AND reduce solar gain by removing the glass !!

    keep doing this till you reach the temperature you require everybody's happy;-)

    I'll get me coat....

    Cheers

    Richard

  3. #3
    Join Date
    May 2004
    Location
    England
    Age
    53
    Posts
    111
    Rep Power
    20

    Re: Selection Opinions.

    Quote Originally Posted by rbartlett

    I'll get me coat....
    Bit hot for that isn't it?

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Selection Opinions.

    if you're ducting in fresh air would a 25kW rooftop not suffice, or have i miscalculated......

    Al

  5. #5
    rbartlett's Avatar
    rbartlett Guest

    Re: Selection Opinions.

    if I read it right. You're looking at 150+kw depending upon the things I don't know

    either way if there is such a glass wall they will end up shading it as people will not be able to work at p.c's etc

    the temp will need to be kept 20 or below and the air should have a high movement to reduce the feeling of the sun -bit like when you drive in the car

    cheers

    richard

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Selection Opinions.

    Quote Originally Posted by al
    if you're ducting in fresh air would a 25kW rooftop not suffice, or have i miscalculated......

    Al
    Hmmmm

    200 people at 90w sensible = 18kw
    200 people at 50w latent = 10kw
    200 people at 12 l/s (t1 -t2) (35 -21) = 58.13kw
    Lighting = (25 x 8.5 x 2 x 15w/m2) = 6.38kw
    Solar = ?
    Fabric gains = ?
    Infiltration = 3.93kw based on 0.5 air changes per hour
    Equipment = ?


    25kw might be a tad undersized
    Last edited by frank; 19-07-2006 at 09:41 PM.

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Selection Opinions.

    no wonder my stuff never works........and i thought it was because it was LG

  8. #8
    Join Date
    May 2004
    Location
    England
    Age
    53
    Posts
    111
    Rep Power
    20

    Re: Selection Opinions.

    Quote Originally Posted by rbartlett
    either way if there is such a glass wall they will end up shading it as people will not be able to work at p.c's etc
    Sorry, not enough detail from me, they want to turn the building shell into an art gallery. They have suggested exposed cassettes or ducted fancoils.

    I hope it's modern art, so i can just throw the stuff in, have it look like a dogs diner, and call it 'Art' might even be able to sell it onto the Tate Modern if i call it 'Twisted metal of my fried brain' and call my self 'Sergio the tortured' (apologies to anyone called Sergio the tortured

    i'm getting just over 200kW at design temps, but don't currently have enough room for that much equipment, looks like a new plant room coming.

  9. #9
    Join Date
    Jan 2006
    Location
    Surrey
    Posts
    26
    Rep Power
    0

    Re: Selection Opinions.

    I think that you need to be a bit more realistic.

    Is it likely that the gallery will have an occupancy of 200 people when the ambient temp is 35°C? I would imagine that a gallery gets the most busy in the evenings (for shows etc.) when the ambient temp has dropped considerably. I would also guess that 200 people does not occur every day.

    The AHU should also have some sort of heat recovery function between extract and supply (usually about 75% efficient). This will reduce the amount of AC plant accordingly.

  10. #10
    Join Date
    May 2004
    Location
    England
    Age
    53
    Posts
    111
    Rep Power
    20

    Re: Selection Opinions.

    Hi Jez,

    I fully accept the sensible factor, and heat recovery is a must. i personally feel it's for the client to factor in the variables of how many people and when. to be fair to them, it will get a lot of use both during the day and evening.

    i'm always very cautious about doing too much factoring on the clients behalf, i've been caught out before, and as such always state my design conditions for them to approve.

  11. #11
    Join Date
    Jan 2006
    Location
    Surrey
    Posts
    26
    Rep Power
    0

    Re: Selection Opinions.

    It's always good to discuss it with them. They may be looking for guidance and are unsure themselves.
    You could always do a selection for 'worst case' and 'likely case' and as you say, state your assumptions for each option.

  12. #12
    Join Date
    May 2004
    Location
    England
    Age
    53
    Posts
    111
    Rep Power
    20

    Re: Selection Opinions.

    I take your point Jez, maybe i'm just tired of the 'i want the best duty for lowest price' rather than best option.

    Mentioning no names, i decided to ask a manufacturer to do some calcs and selections, earn their money. well having lost three days, it was all wrong, cassettes rather than ducted, no central control, and having done an AutoCAD drawing of the site and plant area, i asked how they propose to have VRF condensing units with 20mm clearance all round???

    Give up

    Any suggestions of a manufacturer who doesn't just give you the manuals and has an ounce of common sense?

Similar Threads

  1. Capillary Tube Selection
    By lana in forum Commercial
    Replies: 17
    Last Post: 12-03-2009, 05:57 PM
  2. HELP PLZ: Shell & Tube Selection Parameters
    By Mahmoud in forum Fundamentals
    Replies: 5
    Last Post: 01-02-2008, 01:04 AM
  3. piping selection for R404A
    By drk_in in forum Tools and Calculators
    Replies: 5
    Last Post: 14-11-2005, 06:33 AM
  4. TEV selection
    By Lc_shi in forum Fundamentals
    Replies: 9
    Last Post: 13-10-2005, 02:56 AM
  5. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •