    Cellar trip



    Went out to a cellar , condensing unit stopped.......
    Had tripped on head pressure control.......
    Was a standard NRS Cellar , running on R407C
    Tripped at 300psi

    When I looked at the fins..........it had a thick coat of fur.......was absolutely disgusting.

    Then I noticed all the dog food. Dogs had the run of the place. Dog hairs got sucked up into the coil.....I think they slept directly under the condensing unit

    I washed it down. blew off.......got the coil cleared. Fortunately a water hose was right beside it.

    Got some dog hairs into my mouth............Yurghhhhhhhh

    Ran unit up............down to a nice 250psi in a 30C ambient



  2. #2
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Cellar trip

    was it a blocked haired condensing terrier ???

  3. #3
    Join Date
    Aug 2005
    Location
    manchester
    Age
    47
    Posts
    18
    Rep Power
    0

    Re: Cellar trip

    Had that problem loads of times. Went to one pub to find that fault. Landlord told me he didnt have a dog!!! But I just laughed!
    He wasn't allowed Pets in the pub! lol.
    :eek:

  4. #4
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Cellar trip

    300psi is to low for 407c hp switch.
    Takes a licking, keeps on ticking.

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Cellar trip

    Quote Originally Posted by slingblade
    300psi is to low for 407c hp switch.

    Bearing in mind that day the outside ambient was hovering around the 35C mark, I thought it was a bit low as well.

    I did not change the setting as didnt want to fiddle with what the installation engineer had set it up as.

    As after the clean it hovered around 250/260 psi, I was content and left it at that.

    What should the HP be set at Sling.........for my future reference

    Thx

  6. #6
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Cellar trip

    90% of blow off valve setting is a general rule of thumb for hp. an nrs cellar cooler will not have one obviously. i would say that r22 hp is around 350 psig in my experience and as such 407 should be a bit higher. i would get a comparator and look into it further with regards to temp/pressures, but ive had a long day. im sure one of the book worms here will have all the relevant correct ashrae info or some such thing but 350-375 psig suits me.
    Takes a licking, keeps on ticking.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Cellar trip

    but 350-375 psig suits me.
    I'd agree with that

  8. #8
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Cellar trip

    Quote Originally Posted by frank
    I'd agree with that
    Whooohoooo. i got one right.
    Takes a licking, keeps on ticking.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Cellar trip

    Steady on now

  10. #10
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Cellar trip

    Quote Originally Posted by slingblade
    Whooohoooo. i got one right.
    Outstanding work

  11. #11
    Join Date
    Jun 2006
    Location
    UK
    Posts
    25
    Rep Power
    0

    Re: Cellar trip

    Back in the early 80's when all pubs had dogs, this was normal. now we live in this sterile dump.

  12. #12
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Cellar trip

    When I got to the pub, the landlord went upstairs and locked the dogs in one of the upstairs rooms.

    Access to the condenser unit was on the first floor on a balcony.

    Each time I went up the stair, or came down to pick up some kit, the dogs growled.

    I kept having fears that "what if" the door inadvertently opened.......I would have a pack of rottweilers destroy this one long served , talented, humurous fridgy.......in one snarly snap of jaws.

    My blood pressure rocketed............Im sure

    Boy or boy, was I glad to be out of that god forsaken place........

    Now..........if it were cats......................mmmmmm

Similar Threads

  1. cellar cooler with a/.c condenser
    By rbartlett in forum Air Conditioning
    Replies: 5
    Last Post: 01-03-2006, 10:56 PM
  2. MV600 head pressure trip (ghost)
    By andre_fridge in forum Technical Discussions
    Replies: 9
    Last Post: 28-01-2006, 02:16 PM
  3. Cellar cooler in the 'Vic
    By shanes696 in forum Commercial
    Replies: 6
    Last Post: 19-12-2005, 10:43 PM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. IMI Marstair Cellar Cooler
    By Abe in forum Trouble Shooting
    Replies: 25
    Last Post: 20-03-2004, 02:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •