19-07-2006, 11:34 AM #1
Cellar trip
Went out to a cellar , condensing unit stopped.......
Had tripped on head pressure control.......
Was a standard NRS Cellar , running on R407C
Tripped at 300psi
When I looked at the fins..........it had a thick coat of fur.......was absolutely disgusting.
Then I noticed all the dog food. Dogs had the run of the place. Dog hairs got sucked up into the coil.....I think they slept directly under the condensing unit
I washed it down. blew off.......got the coil cleared. Fortunately a water hose was right beside it.
Got some dog hairs into my mouth............Yurghhhhhhhh
Ran unit up............down to a nice 250psi in a 30C ambient
-
19-07-2006, 04:54 PM #2
Re: Cellar trip
was it a blocked haired condensing terrier ???
-
19-07-2006, 09:35 PM #3
Re: Cellar trip
Had that problem loads of times. Went to one pub to find that fault. Landlord told me he didnt have a dog!!! But I just laughed!
He wasn't allowed Pets in the pub! lol.:eek:
-
20-07-2006, 09:58 AM #4
Re: Cellar trip
300psi is to low for 407c hp switch.
Takes a licking, keeps on ticking.
-
20-07-2006, 12:21 PM #5
Re: Cellar trip
Originally Posted by slingblade
Bearing in mind that day the outside ambient was hovering around the 35C mark, I thought it was a bit low as well.
I did not change the setting as didnt want to fiddle with what the installation engineer had set it up as.
As after the clean it hovered around 250/260 psi, I was content and left it at that.
What should the HP be set at Sling.........for my future reference
Thx
-
20-07-2006, 09:00 PM #6
Re: Cellar trip
90% of blow off valve setting is a general rule of thumb for hp. an nrs cellar cooler will not have one obviously. i would say that r22 hp is around 350 psig in my experience and as such 407 should be a bit higher. i would get a comparator and look into it further with regards to temp/pressures, but ive had a long day. im sure one of the book worms here will have all the relevant correct ashrae info or some such thing but 350-375 psig suits me.
Takes a licking, keeps on ticking.
-
20-07-2006, 09:15 PM #7
Re: Cellar trip
but 350-375 psig suits me.
-
20-07-2006, 09:21 PM #8
Re: Cellar trip
Originally Posted by frankTakes a licking, keeps on ticking.
-
20-07-2006, 09:23 PM #9
Re: Cellar trip
Steady on now
-
20-07-2006, 09:44 PM #10
Re: Cellar trip
Originally Posted by slingblade
-
20-07-2006, 09:58 PM #11
Re: Cellar trip
Back in the early 80's when all pubs had dogs, this was normal. now we live in this sterile dump.
-
21-07-2006, 11:32 AM #12
Re: Cellar trip
When I got to the pub, the landlord went upstairs and locked the dogs in one of the upstairs rooms.
Access to the condenser unit was on the first floor on a balcony.
Each time I went up the stair, or came down to pick up some kit, the dogs growled.
I kept having fears that "what if" the door inadvertently opened.......I would have a pack of rottweilers destroy this one long served , talented, humurous fridgy.......in one snarly snap of jaws.
My blood pressure rocketed............Im sure
Boy or boy, was I glad to be out of that god forsaken place........
Now..........if it were cats......................mmmmmm
Similar Threads
-
cellar cooler with a/.c condenser
By rbartlett in forum Air ConditioningReplies: 5Last Post: 01-03-2006, 10:56 PM -
MV600 head pressure trip (ghost)
By andre_fridge in forum Technical DiscussionsReplies: 9Last Post: 28-01-2006, 02:16 PM -
Cellar cooler in the 'Vic
By shanes696 in forum CommercialReplies: 6Last Post: 19-12-2005, 10:43 PM -
Searle cellar cooler control problem
By iceman007 in forum ElectricalReplies: 6Last Post: 06-07-2004, 08:57 PM -
IMI Marstair Cellar Cooler
By Abe in forum Trouble ShootingReplies: 25Last Post: 20-03-2004, 02:03 PM