    Trane Screw comps



    Got a couple Trane chillers with CHHB1007NG0N119A helix screw compressors. All 4 compressors are reading 13 to 9 mega ohms to ground @ 500V. I find it odd all 4 would be reading such a low mega ohm. And none showed any acid.
    Do these just use mag. wire with poor insulation or what?

    M# RTAA2004XG01A1DOB


    Will melt ice for $101/hr

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Trane Screw comps

    Off the top of my head I'd say this sounds like the system is wet. Have you checked the site glass to see the moisture indicator color?

    Perhaps they have only been this way for a short time, and acid has not developed yet?

  3. #3
    Join Date
    Feb 2006
    Location
    WA, USA
    Posts
    62
    Rep Power
    19

    Re: Trane Screw comps

    Always... As green as the top bar on these forum posts. Hence my curiosity as to why.
    Will melt ice for $101/hr

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Trane Screw comps

    Ok, now I'm going out on a limb.

    Is the area around the motor terminals wet from condensation? In the past I had the unfortunate experience to work on some Dunham-Bush equipment that caused me to learn a lot of different things to solve the problems.

    One of those was the motor terminal box was always wet from condensation due to the cold suction return gas through the motors (semi-hemetic).

    You couldn't get decent megger reading for nothing.

    Shut the compressors off, went to a store to get a hair dryer. Shut off the power, and removed all of the electrical connections and terminal blocks. Dried all of the terminals, terminal blocks, etc.

    Used a spray on electrical sealer around the terminals and all over the inside of the terminal enclosure being careful to not get any spray on the terminal posts.

    Used the hair drier to speed up the curing process on the sealer.

    When the sealer was hard, I re-installed all of the wiring, etc.

    Meg the motors and guess what? A decent reading. None of the low stuff like you are experiencing.

    Now, I'm not saying that's the solution to your problem, but it did solve mine.

    Hope that helps.
    Last edited by US Iceman; 20-07-2006 at 02:59 PM.

  5. #5
    Join Date
    Feb 2006
    Location
    WA, USA
    Posts
    62
    Rep Power
    19

    Re: Trane Screw comps

    Possible.. however don't remember seeing any sweating in the terminal boxes. I'll look at it again when I change out a cond. fan.
    Will melt ice for $101/hr

  6. #6
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: Trane Screw comps

    I would suggest iceman is correct,i think the terminal box sits horizontal on top of the compressor & if the terminal box lid is leaking you will get tracking. A similar problem used to happen with the carrier 06D box which would fill up with water, you'll come along find the contcator blown to peices but the compressor windings fine. I've seen those trane screws with about 1/2 inch of water in the box. Also with the RTAA or RTAB if you get HP trips in winter & LP trips in summer we used to fit an HP switch to 1st stage condensing fan as UCM uses the saturated condensing temperature sensor which can be wildly inaccurate at start up until system settles down.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Screw comps

    I think the terminals were tightened over their rated torque, and the bolts cracked the insulation laquer where the bolts cross through.
    It once happened to me, and I almost got mad trying to sort out why that compressor was not passing the electrical stiffness test.
    Also do the meg testing WITH gas, because vacuum is a good conductor.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Trane Screw comps

    Quote Originally Posted by NoNickName
    I think the terminals were tightened over their rated torque, and the bolts cracked the insulation laquer where the bolts cross through.
    That's another very good possibility too. It's essentially the same problem.

    Chris Burton mentioned "tracking". That's a term I have not heard for quite some time. I have seen this in contactors too. In that case I believe it was called carbon tracking. Sometimes you can see a very faint line from one pole to another.

    This is similar also to flash arcs across the starter contacts. When you look at the front of a starter, the contacts have a little plastic shield/plate over them. This is the flash guard to prevent arcing across the contact. Say L1 to L2, etc.

    Does the EU have anything for flash suppression on large motor starters or switchgear? There has been a BIG push here to train people on this, and prevention methods.

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Trane Screw comps

    Yes, they call it "flame chimney", and they are commonly found on big contactors.

Similar Threads

  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Replies: 14
    Last Post: 20-02-2011, 12:10 AM
  2. do u have any data on comparison of single screw and twin screw?
    By vuputuri in forum Technical Speculations
    Replies: 5
    Last Post: 22-02-2008, 03:52 PM
  3. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Replies: 43
    Last Post: 12-09-2006, 03:19 AM
  4. screw compressor failure
    By aygul in forum Trouble Shooting
    Replies: 23
    Last Post: 09-12-2004, 09:09 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •