    Daikin EUWA50 Chiller



    Has anyone worked on an EUWA50 chiller?

    I had a high pressure problem which I sorted out but then the oil switch light started showing without the chiller even running. The wiring circuit was extremely difficult to follow. Couldn't get the thing to run.

    Returned next day to start affresh. Switched on and it worked first time.

    What's going on?

    Cheers

    PB



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Daikin EUWA50 Chiller

    I haven't worked on one of these chillers, but the problem you described sounds like it is wiring related.

    Did the oil safety trip after the high pressure switch tripped?

    If so, the opening of the high pressure switch must have energized the resistance heater in the oil safety switch.

    That should be fun to sort out it that's the case.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •