    Indoor coil capacity?



    Can anyone estimate for me the cooling rating for this indoor coil? It measures 20" x 40" with four rows of 3/8" copper lines. The fins are aluminum and probably 14 per inch. It's a flat slab coil, mounted diagonally in the blower case. The blower is capable of 1650 CFM air flow.

    Air outlet is roughly 23" x 24". Air inlet is around 23" x 33".

    It is currently fitted with a 3 ton txv. I'm wondering if this can be fitted with a 5 ton txv and a 5 ton condensor unit outdoors. Lines are 3/8" and 7/8".


    I have a simlar question concerning the outdoor coil. It has 32" x 80 " of coil wrapped around the outdoor fan. It's constructed with two rows of copper lines, 64 tubes top to bottom across 32".



  2. #2
    Join Date
    Jun 2006
    Location
    India
    Age
    63
    Posts
    28
    Rep Power
    0

    Re: Indoor coil capacity?

    Quote Originally Posted by Larry2
    Can anyone estimate for me the cooling rating for this indoor coil? It measures 20" x 40" with four rows of 3/8" copper lines. The fins are aluminum and probably 14 per inch. It's a flat slab coil, mounted diagonally in the blower case. The blower is capable of 1650 CFM air flow.

    Air outlet is roughly 23" x 24". Air inlet is around 23" x 33".

    It is currently fitted with a 3 ton txv. I'm wondering if this can be fitted with a 5 ton txv and a 5 ton condensor unit outdoors. Lines are 3/8" and 7/8".


    I have a simlar question concerning the outdoor coil. It has 32" x 80 " of coil wrapped around the outdoor fan. It's constructed with two rows of copper lines, 64 tubes top to bottom across 32".
    Your coil is suitable for 6 TR capacity for normal AC application and the condenser capacity is 7 TR.

    Presently you are not utilizing its full capacity. TXV-5 is suitable.

  3. #3
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Re: Indoor coil capacity?

    Thanks very much.

Similar Threads

  1. R-407C and Coil Capacity
    By glabah in forum Refrigerants
    Replies: 5
    Last Post: 03-06-2006, 11:36 AM
  2. Capacity achievement
    By Hemant Anand in forum Industrial
    Replies: 8
    Last Post: 18-12-2005, 01:18 AM
  3. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM
  4. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM
  5. Relative Power / Capacity data
    By Argus in forum Air Conditioning
    Replies: 3
    Last Post: 01-08-2002, 09:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •