    Ground source heat & air?



    If one wanted to contruct a ground source system of five tons capacity, how large would the field need to be? I'm talking about using a horizontal array of piping, burried 5-1/2 to 6 foot deep. I'm thinking a backhoe operator could knock out trenching a field in a day; the task would be quite similar to construction of a septic tank field. A backhoe would cost maybe $60-$70 per hour.

    I read of grouting vertical systems to improve heat transfer. Would one also grout an array of buried pipe for the same reason?

    What does the pipe, fittings, equipment and that sort of thing cost? I'm thinking the high prices I see for these systems are because of limited relection of contractors. Maybe it's wishful thinking on my part.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Ground source heat & air?

    It depends on the type of soil. Normal moist soil is capable of releasing 20Watts per linear meter of pipe at 1.8 meters in the underground and pipes 0.7 meters apart, but for a maximum extraction of 1800 kWh/year for heating only and 2400 kWh/year for heating and cooling.

    Boreholes ground heat collectors can release 50-100Watts per meter per borehole.

    Costs are approx 1000-1500 euro per 200mm diam. drilling, including grouting with bentonite. Costs may increase in case of sand or stone soil.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Ground source heat & air?

    I have some books of the IGSHPA.
    Where are you living in the US?
    For a common house, making the trenches can be done in 1 day.
    Some rules if installed horizontally, take 5 to 7 times the surface of the house.
    +/- 2kW for a verticla borehole.
    Horizontal trenches are normally backfilled with the ground taken out the trench. No additional thermal enhanced grouting.
    Slinky loop is also possible.
    You can use normal PE3408 Pipe and weld it yuourself with a mirror welder (don't know the correct English expression for it)
    Don't make the pipe runs too long.
    Parallel systems, use one loop for each ton of heat pump capacity.
    You can install more then one pipe in a trench.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Ground source heat & air?

    It depends on where you are as to how much pipe, how long the trenches are but don't waste your time with a mickey mouse backhoe. A machine that costs twice as much will dig 4 times as fast.

  5. #5
    Join Date
    Jun 2006
    Location
    USA
    Posts
    204
    Rep Power
    18

    Re: Ground source heat & air?

    Thanks everyone. It seems the trench system required would be more extensive than I first thought. I found some data for the States at http://www.geokiss.com/ and it would cost more installation price than I imagined.

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  3. Ground source heat pump
    By Cooler in forum Domestic
    Replies: 1
    Last Post: 29-07-2006, 08:51 PM
  4. Ground source heat pump
    By Lc_shi in forum Refrigeration Books
    Replies: 7
    Last Post: 18-04-2006, 04:30 PM
  5. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •