Results 1 to 8 of 8
-
14-07-2006, 08:33 PM #1
Head Pressure: How High is Too High?
Head pressure should correspond to the pressure of ambient plus 30-35F. My question is, how high above this psig is cause for alarm? If the compressor isn't overheating and the system is cooling, but the head pressure is 20-25 psig higher than it's supposed to be, is that worth worrying about?
-
14-07-2006, 09:05 PM #2
Re: Head Pressure: How High is Too High?
Hi HHC,
Welcome to the RE forums.
Head pressure should correspond to the pressure of ambient plus 30-35F.
I think for the most part you can "assume on newer air-cooled systems" the difference would be closer to 15-20 degrees above the highest ambient. (I'm using the Fahrenheit scale here). This depends on how the system was designed, so these are really guesses without that detail.
As a "general rule" this might be a good way to initially evaluate a system. If the discharge pressure is higher than the refrigerant saturation temperature of ambient temp. + 20 degrees, this would mean something is not quite right.
Dirty condenser, worn fan belts, etc.
Anytime the discharge pressure is higher than it needs to be you are using excess energy and increasing the stresses placed on the compressor. You are also loosing some cooling capacity doing this.
Is it worth worrying about?... I would look into it if it was me.
-
14-07-2006, 10:27 PM #3
Re: Head Pressure: How High is Too High?
Thanks for the quick reply. The unit is a 20+ year old Beverage-Air 3-keg direct draw beer cooler running R12, fan cooled, with a new hermetic compressor. Condenser is clean, but does have some rust on it.
With regard to increasing stress on the compressor, would this be reflected in the amperage? My amp readings show it to be about 6.3 amps; the compressor is rated at 6.7.
-
14-07-2006, 11:11 PM #4
Re: Head Pressure: How High is Too High?
If the condenser was able to have cooler air flowing through it, the discharge pressure should decrease. That would reduce the amp draw.
If the compressor was recently changed, was the system evacuated with a vacuum pump? If the system has air in it, the discharge pressure may be higher than normal also.
The discharge pressure may be a bit higher also due to pull down load with a warm box.
It's hard to troubleshoot something you can't see or hear.
-
14-07-2006, 11:39 PM #5
Re: Head Pressure: How High is Too High?
Yes, a vacuum pump was used, but I don't think it was adequate. It was an older single-stage pump. Do you have any estimation of how much pressure could be attributable to a small amount of air in the system?
By the way, the cabinet is cooling adequately (cuts in at 40F and cuts out at 32F); all readings are being taken at the end of the cooling cycle, just before the compressor cuts out.
A point worth noting is that even with the head pressures described, the suction is reading between 10-14 psig.
-
15-07-2006, 04:19 AM #6
Re: Head Pressure: How High is Too High?
Originally Posted by HHC
1) Record the discharge pressure
2) Measure the liquid refrigerant temperature leaving the condenser.
3) Find the pressure for the saturation temperature for R-12 liquid.
4) Subtract the pressure for the liquid temperature from the discharge pressure.
The difference in pressure may be attributed to non-condensables (air, etc.) or subcooling.
Since it is hard to tell the difference between subcooling or non-condensables at this point you have two options.
1) recover the refrigerant from the system, and completely evacuate the system.
or,
2) let it run as is. If the system is cooling OK you might be spending more money fixing something than it may be worth.
-
15-07-2006, 10:19 AM #7
Re: Head Pressure: How High is Too High?
Originally Posted by HHC
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes:
-
15-07-2006, 05:23 PM #8
Re: Head Pressure: How High is Too High?
Originally Posted by US Iceman
By the way, condenser subcooling is running between 21-24F.
Thanks again for the great input!
Similar Threads
-
MV600 head pressure trip (ghost)
By andre_fridge in forum Technical DiscussionsReplies: 9Last Post: 28-01-2006, 03:16 PM -
Reading High Head Pressure
By Abe in forum CommercialReplies: 10Last Post: 15-01-2006, 03:48 PM -
High pressure reading before and after condenser coil
By Cofreth in forum RefrigerantsReplies: 6Last Post: 18-11-2005, 05:30 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM