    Freezing problem



    Hi guys ,

    I have a problem thats been thats been puzzling me , i have a room that needs to be cooled to +6*C , and 6 evaporators in that room on the ceeling , 5 of them are 3.2 kw and one is 2.4 kw , and i'm using a compressor thats 12.4 kw -10*C and the problem is that none of the evaporators are freezing , only the pipes near the Thermo Expansion Valve are freezing . The lenght of the pipes from the compressor to the evaporators are 50meters , does this has something to do with the TEV ? because i just cant figure out why the evaporators arent freezing ?



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Freezing problem

    Quote Originally Posted by MajinDave
    Hi guys ,

    I have a problem thats been thats been puzzling me , i have a room that needs to be cooled to +6*C , and 6 evaporators in that room on the ceeling , 5 of them are 3.2 kw and one is 2.4 kw , and i'm using a compressor thats 12.4 kw -10*C and the problem is that none of the evaporators are freezing , only the pipes near the Thermo Expansion Valve are freezing . The lenght of the pipes from the compressor to the evaporators are 50meters , does this has something to do with the TEV ? because i just cant figure out why the evaporators arent freezing ?
    What is the evaporation pressure at the coolers, it may be above freezing, if you measure this and the temperature at the cooler outlets it should tell you all you need to know


    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Freezing problem

    Quote Originally Posted by Andy
    What is the evaporation pressure at the coolers, it may be above freezing, if you measure this and the temperature at the cooler outlets it should tell you all you need to know


    Kind Regards Andy

    Or to put it another way with the load you have on the compressor and the long suction line the evaporation probably is above freezing.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    MajinDave's Avatar
    MajinDave Guest

    Re: Freezing problem

    Well i tested and there is good pressure at the end of the line , in the next room there are same evaporators only smaller 1.5 kw , and it freezes and gives great result , but with these evaporators i just cant figure it out why they wont freeze , the others do , and they are in about the same distance from the compressor + - 50 meeters

    and i tryed shutting half of the evaporators in the room , eaven tryed running 1 at a time and still nothing .

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Freezing problem

    Quote Originally Posted by MajinDave
    Well i tested and there is good pressure at the end of the line , in the next room there are same evaporators only smaller 1.5 kw , and it freezes and gives great result , but with these evaporators i just cant figure it out why they wont freeze , the others do , and they are in about the same distance from the compressor + - 50 meeters

    and i tryed shutting half of the evaporators in the room , eaven tryed running 1 at a time and still nothing .
    Good pressure means nothing
    What is your evaporation at the coolers.
    What is the subcooling off the condenser

    Lack of subcooling could also cause this, could be mostly gas going through the expansion valves not liquid.


    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Freezing problem

    MajinDave,

    When you ask for help it would be nice to include some basic information for us so that we can understand your problem.

    As Andy said, good pressure doesn't mean anything. What refrigerant are you using in this system? What is the suction pressure at the compressor?

    I'm also questioning why the compressor is designed for -10C suction and the room is at +6C. That seems like a lot of difference!

    If the evaporator coils were sized for a 6 degree temperature difference, that would still put the evaporating temperature at about 0C. At this temperature I doubt the coils would frost much anyway.

    Is the problem new, or has it been going on for some time?

  7. #7
    MajinDave's Avatar
    MajinDave Guest

    Re: Freezing problem

    Quote Originally Posted by US Iceman
    MajinDave,

    When you ask for help it would be nice to include some basic information for us so that we can understand your problem.

    As Andy said, good pressure doesn't mean anything. What refrigerant are you using in this system? What is the suction pressure at the compressor?

    I'm also questioning why the compressor is designed for -10C suction and the room is at +6C. That seems like a lot of difference!

    If the evaporator coils were sized for a 6 degree temperature difference, that would still put the evaporating temperature at about 0C. At this temperature I doubt the coils would frost much anyway.

    Is the problem new, or has it been going on for some time?
    US Iceman

    I'm using R-22 , the suction pressure is 1.6 bar , i was explaining that the room has to be cooled to 6* , and the compressor is 12kw at -10 , i'm using 1 compressor for 6 evaporators each ~ 3kw .
    This has been going on for a month now , and the room's temp hardly drops below 16*

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Freezing problem

    Quote Originally Posted by MajinDave
    US Iceman

    I'm using R-22 , the suction pressure is 1.6 bar , i was explaining that the room has to be cooled to 6* , and the compressor is 12kw at -10 , i'm using 1 compressor for 6 evaporators each ~ 3kw .
    This has been going on for a month now , and the room's temp hardly drops below 16*
    Obviously a mis-matched system. 6 x 3kw evaporators = 18kw indoor load connected to a 12kw compressor

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Freezing problem

    Make a little sketch of the setup and post it here.
    Length and diameters lines, what valves and orifice, type of evaporators, type of compressor, (1 TEV) condensor, measured pressures, ....
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Freezing problem

    For a system using R-22 and a suction pressure of 1.6 bar (I'm assuming gauge pressure) the saturation temperature for that pressure is -18.3C.

    Something is not right. Besides the comment Frank added too (which bothered me also).

    Did the lack of cooling start when the weather started to get warmer?

    With 150 meters of refrigerant tubing, my guess would be the liquid line has a lot of flash gas in it, reducing the system capacity.

    Does the liquid line travel up to the evaporators? How high does the liquid line go?
    Does the liquid line travel through a hot space before reaching the evaporators?
    Last edited by US Iceman; 15-07-2006 at 12:40 AM.

  11. #11
    Join Date
    Jun 2006
    Location
    los CaBOS MEXICO
    Age
    63
    Posts
    5
    Rep Power
    0

    Re: Freezing problem

    we need to know if every thing match.....
    compressor model.......
    amps, voltage and phases......
    evaporator model.......
    TXV number.............
    refrigerant pressures.....
    discharge.....
    suction.......
    pipe temperatures at low side...
    subcoolong and superheat....

Similar Threads

  1. York Screw Oil Problem
    By tomt in forum Technical Discussions
    Replies: 10
    Last Post: 02-12-2009, 02:48 PM
  2. Quick freezing of fresh products
    By maxim971 in forum Technical Speculations
    Replies: 12
    Last Post: 18-09-2009, 11:06 PM
  3. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  4. freezing dog food
    By knighty in forum Fundamentals
    Replies: 26
    Last Post: 27-09-2005, 09:52 PM
  5. LG 10.5 kw cassette timer problem
    By Andy W in forum Air Conditioning
    Replies: 10
    Last Post: 25-06-2005, 07:09 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •