    Volume ratio selection



    Hi all,

    We recently purchased high stage screw compressor that has ability to manually change volume ratio while stationary (2.2 to 5.0) Our contractor informed us they will set the volume ration for 5.0. This does not seem right when you run the numbers out for our operating conditions (28 psig suction, 110 to 150 psia discharge depending on season) Based on my calculations the volume ration should be 2.2 to 2.8 depending on season.

    With a volume ration is 5.0 I believe we are over compressing with an energy penalty. Please comment or confirm



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Volume ratio selection

    Quote Originally Posted by rosetennis
    Hi all,

    We recently purchased high stage screw compressor that has ability to manually change volume ratio while stationary (2.2 to 5.0) Our contractor informed us they will set the volume ration for 5.0. This does not seem right when you run the numbers out for our operating conditions (28 psig suction, 110 to 150 psia discharge depending on season) Based on my calculations the volume ration should be 2.2 to 2.8 depending on season.

    With a volume ration is 5.0 I believe we are over compressing with an energy penalty. Please comment or confirm

    Sounds a little high. You need the installation manual for the compressor to set the VI up

    It's then a compromise, especially if the suction pressure varies such as load pull down.

    28 PSIG is not LT on Ammonia, the figures you give are for an LT compressor.

    A guess on my part would be about 3.5 VI, but again if the compressor is on load pulldown the 5 VI may be fine

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Volume ratio selection

    Hi rosetennis,

    Based on my calculations the volume ration should be 2.2 to 2.8 depending on season.
    If the refrigerant is ammonia (you didn't specify) I arrived at the same Vi range you stated.

    If the suction pressure does not change from 28 psig (a few pounds one way or the other), then the only reason to change the Vi would be the change in discharge pressure.

    One thing you might want to check is the motor amps when the compressor is operating at the two different operating conditions (28/110 & 28/150).

    Set the Vi for 2.2 and run the compressor at 28/110psig. Check the motor amps.

    Set the Vi for 2.8 and run the compressor at 28/150psig. Check the motor amps.

    I suspect if you would dial in the Vi for an average of 2.5, and then run the compressor at the two conditions (fully loaded), the motor amps will not change significantly.

    A Vi of 5 is certainly too high for this range of operation. Unless, the compressor is being used as a swing compressor to run at a lower (much lower) suction pressure. If this compressor is being used as a swing compressor for low temp and high temp, then the Vi control should have been automatic.

  4. #4
    Join Date
    May 2006
    Location
    Chicago
    Posts
    5
    Rep Power
    0

    Re: Volume ratio selection

    thanks all. the system is ammonia. The machine is only a high side machine. Will set the compressor for 2.2 in winter and 2.8 in summer

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Volume ratio selection

    Just be sure to monitor the motor amps. What you really want is the lowest amps at any condition. The actual Vi might be a little higher or lower.

    Remember, the Vi is just an estimate.

Similar Threads

  1. HELP PLZ: Shell & Tube Selection Parameters
    By Mahmoud in forum Fundamentals
    Replies: 5
    Last Post: 01-02-2008, 02:04 AM
  2. Evaporator Selection
    By chooipeng in forum NH3
    Replies: 12
    Last Post: 26-09-2006, 08:11 AM
  3. Air Volume & Ref Cap
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 6
    Last Post: 23-07-2005, 02:50 AM
  4. Compressor's volume efficiency
    By John McGru in forum Fundamentals
    Replies: 0
    Last Post: 16-02-2004, 09:44 AM
  5. selection of centrifugal fan
    By watana in forum Air Conditioning
    Replies: 0
    Last Post: 14-09-2003, 04:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •