    carrier chiller chaos



    Hi chaps hope you can help to ID this electromechanical component in the main panel of this 25 year old system, the system was off on control circuit on arrival, switched on lots of smoke/small fire occured. This is a new customer to myself due to previous contractor/service guys bailing out. The smoke / fire came from this device.
    Attached Images Attached Images
    • File Type: jpg 1.JPG (94.1 KB, 52 views)
    Last edited by bebad; 07-07-2006 at 10:31 AM.



  2. #2
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: carrier chiller chaos

    Looks like a stepping motor.

    Probably used for loading/unloading.
    Last edited by Temprite; 07-07-2006 at 10:39 AM.

  3. #3
    Join Date
    Jul 2005
    Location
    UK
    Posts
    60
    Rep Power
    19

    Re: carrier chiller chaos

    That is a Honeywell stepping motor in a state of some disarray.

    It is driven by a built-in 24 volt transformer. When put together properly, the bits on the front are a small balancing relay that drives the two motors and should be positioned on the side, to the right.

    Fix that before anything else.

    By the looks of it I would say that it is in a 30GA or GB, French made, mid 80’s.
    .
    Sodd's the name...... Law's the game.
    Established 1791 - still going strong.

  4. #4
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: carrier chiller chaos

    Thank you Sir Josh, have you come across one lately(are they still in circulation/stock)? if so, prehaps I may well fix all other prob's! 4 out of 6 comps are dissconnected too.Thanks Temprite too.
    Attached Images Attached Images
    • File Type: jpg 8.JPG (98.9 KB, 34 views)
    • File Type: jpg 9.JPG (89.6 KB, 43 views)

  5. #5
    rbartlett's Avatar
    rbartlett Guest

    Re: carrier chiller chaos

    Quote Originally Posted by bebad
    Thank you Sir Josh, have you come across one lately(are they still in circulation/stock)? if so, prehaps I may well fix all other prob's! 4 out of 6 comps are dissconnected too.Thanks Temprite too.
    This has been hashed about so badly it's pretty much beyond repair. esp if 4 out of 6 comps are disconnected.

    do't think you will work magic as probably every contractor has thought that before. the company isn't interested in keeping the chiller together before so why think he's going to now??

    tell him it's not worth fixing or ask for an open ended P.O and see how far that gets you

    cheers

    richard

  6. #6
    Join Date
    Jul 2005
    Location
    UK
    Posts
    60
    Rep Power
    19

    Re: carrier chiller chaos

    Try to get the model & serial number. The SN should have a date code.

    Judging by the gauges it's a 30HR (water-cooled).

    Everything's repairable, but it's probably not worth it.
    If the comps are shot, you can rebuild them, but it's a performance.

    To answer your question - no, I havent seen one of those for 25 odd years.

    There used to be hundreds about - a Carrier work-horse if ever there was one.
    .
    Sodd's the name...... Law's the game.
    Established 1791 - still going strong.

  7. #7
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: carrier chiller chaos

    i agree with all the comments but they are expensive to replace and sometimes hidden in basements and thats another problem.run the comps one at a time and see if there is gas in them,if thats good you need to check the shell and tube condition,if its gas tight pull the ends off to check its not blocked and servicable,if all thats o/k which i doubt, you can replace the step timer with a more upto date 4 relay timer and pop some delay timers in,best of luck,your gonna need it !!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: carrier chiller chaos

    The other thing to consider with repair/replacement is - Is it worth it with the incoming gas changes, it is no doubt running on R22; not long left.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: carrier chiller chaos

    In my last company just before my time one of these was retro'ed to 407c -what a complete nightmare for both us and the customer.many many thousands later and the thing was a mare

    You're looking at a 25 year old chiller and trying to breathe new life into it. Forget it -whatever the install hassles are they will pale into insignificance when you've changed 4 compressors the whole of the electrics and the thing STILL keeps breaking down.

    Tell the customer sometimes you just gotta let go....

    Cheers

    Richard

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: carrier chiller chaos

    Ya but could it be certified to operate with R-290?

    as for the controller use a programed MCU for the unit with some heavy duty TRIACs utilizing a PIC you could replace the whole panel pretty much, and most small custom PIC builders don't charge much at all to make the circuit and program it. I have a friend in NZ who makes MCU systems for all the world wide High way Corps. if interested in that rout I'll talk to him or you can hunt one down local.

  11. #11
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Exclamation Re: carrier chiller chaos

    thanks all for advise/responces. after not much time considering my next step ; Condemned.

  12. #12
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: carrier chiller chaos

    I've replaced quite a few honeywell wheatstone bridge controllers for an 8 stage jbt electronic thermostat, does help if you have wiring diagram though! Takes about 4 days.

  13. #13
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: carrier chiller chaos

    Look at attatchments, what you see i what you get, a whole world of s**t and then some I'd imagine.
    Have no diagrams for anything.
    Thanks all again though, Paul.

Similar Threads

  1. carrier chiller fault codes
    By al in forum Air Conditioning
    Replies: 7
    Last Post: 20-07-2009, 10:10 PM
  2. Trane & Carrier Chiller Data
    By mustafa in forum Air Conditioning
    Replies: 8
    Last Post: 03-05-2009, 04:10 PM
  3. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM
  4. Chiller Carrier
    By vspiteri in forum Air Conditioning
    Replies: 11
    Last Post: 17-02-2005, 07:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •