    Carel EVD ICE



    Hello,
    EVD ICE display 9. Utracella display alarm ELE. Ultracella output comp and Fans.
    I cannot find in the manual what the number 9 means.
    The valve stays closed.
    After reset (power off) everything worked back fine.
    Anybody knows this?
    Greetings Fernando



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carel EVD ICE

    From the user manual, the only reference to a number 9 display is in the gas table.
    9 means gas type R600a

    https://www.google.com/url?sa=t&sour...q2os8Pohqhr0c-

  3. #3
    Join Date
    Feb 2024
    Location
    Belgium
    Posts
    2
    Rep Power
    0

    Re: Carel EVD ICE

    Yes, i saw that. But it was programmed R744. It does not change himself, i guess.
    I ordered a new one for be sure.