    Fujitsu compressor suspect!!



    First off.......... New to the forum, so hello to you all

    Working on a Fujitsu ceiling cassette (R410a) today. Initially brought up a fault code of which was traced to an lp issue. Low and behold the system hadn't a drop of gas left. Pressure test revealed a small crack to the flared service valve tapped off beneath the 3 way valve. Brazed this. Pressure tested (all fine), then vac'd out, recharge accordingly.

    The base charge was 2400kg (anyone know the maximum pipe run before additional charge??) Suction registered less than 60 psi?!?!?! whilst the liquid completely frosted over on the service port and looked set to freeze further back up the pipe run on the high side....had pulled back lagging to reveal this.

    Thing is.Compressor running, but condenser doing little duty as no heat exchange apparant with the fan blowing in my face it was ambient cool-no warmth whatsoever.
    Suspect internal compressor damage, wondered if it could be a pumping issue??? I checked to see that both valves were back seated and they were. Realise I could do a pump down test on this but wondered if anyones encountered something similar that could save me the time and just write this pot off altogether???

    It was like the compressor had only enough clout to pump to the beggining of the liquid line and go no further. No suction??

    Hope it's not a blockage.

    Any thoughts appreciated.

    Cheers,

    Jon.
    Last edited by phase3; 10-07-2006 at 11:14 PM.



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Fujitsu compressor suspect!!

    frosting on the pre expansion line and low suction usually means low on refrigerant.

    cheers

    richard

  3. #3
    phase3's Avatar
    phase3 Guest

    Re: Fujitsu compressor suspect!!

    Thanks for reply.

    I appreciate that that would be the usual reaction from low gas, however the reason why I was overly cautious about the compressor was because the pot had been running previously with very little gas and was found the first time round red hot and near enough cooked!

    Forgot to add that. Sorry.

    I will double check the pipe run later, as I could have been decieved by this.

    Cheers.

    Jon.

  4. #4
    rbartlett's Avatar
    rbartlett Guest

    Re: Fujitsu compressor suspect!!

    Quote Originally Posted by phase3
    Thanks for reply.

    I appreciate that that would be the usual reaction from low gas, however the reason why I was overly cautious about the compressor was because the pot had been running previously with very little gas and was found the first time round red hot and near enough cooked!

    Forgot to add that. Sorry.

    I will double check the pipe run later, as I could have been decieved by this.

    Cheers.

    Jon.
    frosting is either as I say or a restriction in the drier/filter capilary section.



    Cheers

    Richard

  5. #5
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Fujitsu compressor suspect!!

    I had a Fujitsu cassette last year with 2 filter driers behind the compressor and both were blocked, a real swine to get to.

  6. #6
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Fujitsu compressor suspect!!

    Phase 3; cooked the oil from running with no gas, always blocks dryer, no Low Pressure switches on these systems, once comp goes out on over temp this system won't restart UNLESS, and this has happened to me before, the customer resets mains to system and restarts operation, they then think they've FIXED it!
    Continually resetting mains when over temp of comp occurs, should the case be so, forget it. Whole new system required, you will be there forever trying to retrieve cooked oil from dozens of blocked filter dryer changes.
    Ps. there's only one dryer in this system and all other Fujitsu splits as far as I'm aware.

    finally, does suction gauge conected to suction service port on Cond. hold a vacuum or take a long time (hours) to equalize?
    Also is this a 3phase system, 3phase????

  7. #7
    Join Date
    Jul 2006
    Location
    England
    Age
    57
    Posts
    18
    Rep Power
    0

    Re: Fujitsu compressor suspect!!

    Phase 3. Why would a low suction pressure and frosting on the low pressure liquid line make you think the compressor might be on it's last legs???

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2007, 09:06 PM
  3. Fujitsu
    By Abe in forum Air Conditioning
    Replies: 9
    Last Post: 21-07-2006, 08:36 AM
  4. Fujitsu Password
    By sigorst in forum Air Conditioning
    Replies: 0
    Last Post: 02-01-2006, 09:56 PM
  5. Fujitsu hp's icing
    By rbartlett in forum Air Conditioning
    Replies: 8
    Last Post: 08-01-2005, 09:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •