    Daikin problem



    Wonder if anyone can help, as daikin tech cant seem to help!

    Was working on a RCY100L7W1 outdoor unit, three phase. Went to site to re-comission system but once power was turned back on nothing happend. PCB had gone down. Changed PCB but still nothing. Tested current on wiring center and that was fine, all 3 phases there. Problem was with the transformer. So iv now changed that. switched it on and the LED on the PCB was constantly flashing, indicating a faulty PCB according to the wiring diagram. Daikin can not suggest anything it may be and im stumped.

    Still have all three phases on the supply and at least now power is getting to the PCB. have nothing on 123E terminal. Only suggestion iv had is the indoor PCB but i cant see it being that as im not getting power leaving the unit.

    Any suggestions would be greatly appreciated!



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin problem

    RCY100L7W1
    Never heard of this unit

    The rest of the code I understand.

    L = version number
    W1 = three phase
    100 = 10 kw

    RCY = ??

    R = outdoor unit

    RY = heat pump

  3. #3
    Join Date
    Nov 2005
    Location
    london
    Age
    37
    Posts
    6
    Rep Power
    0

    Re: Daikin problem

    i meant RYC100L7W1.

  4. #4
    Join Date
    Apr 2006
    Location
    guildford,surrey,uk
    Posts
    6
    Rep Power
    0

    Re: Daikin problem

    there might be an `emergency operation` switch at the top of the outdoor board try that and see if it runs,you have to reset the power when you alter this switch, also have you tried swapping over 2 of the phases

  5. #5
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    45
    Posts
    54
    Rep Power
    19

    Re: Daikin problem

    try unplugging fan motor,
    have had a similar problem and the fan motor was at fault.

    also you say you have three phases - but do you have a neutral, this is v important as pcb will blow without it (500V varistor on board)

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  3. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  4. Daikin FH series problem
    By pdingle in forum Air Conditioning
    Replies: 7
    Last Post: 13-08-2006, 06:45 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •