    New Ammonia System



    Good Day,


    I have extensively searched the internet for information regarding the newly installed ammonia system. I am inquiring about the required pressure for conducting a leak test and the recommended duration for the system to stand during the leak test.
    Additionally, I am seeking information on the vacuum procedure and NH3 charge procedure. I would greatly appreciate it if you could share the relevant details here.


    Thank you.



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: New Ammonia System

    Hi
    First system should be dry by N2 or dry air.

    As much as you can system should be vacuumed
    Time of that 24 h up to 48 hours

    For testing system leak in system should be 1.5 times more than high pressure for NH3 about 25 bars for 48 hours
    Last edited by mbc; 05-02-2024 at 04:42 AM.

  3. #3
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: New Ammonia System

    Thank you for responding to my comment,
    The next step is to charge ammonia into the system. Kindly share the details in sequence.
    Thanks.

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: New Ammonia System

    Hi
    Liquid NH3 should charge to liquid separator
    smoothly
    And in same time check leaks and smell of NH3 in all areas.

  5. #5
    Join Date
    Aug 2022
    Location
    United States
    Posts
    28
    Rep Power
    0

    Re: New Ammonia System

    Shaaf, with all respect, I suggest that if you are not familiar with the procedures of pressure testing, or especially charging ammonia into the system, you need to find or hire someone who is, and not rely on the generic information you will receive from this forum. Both of those procedures are inherently dangerous and potentially deadly.

    Best regards,
    MrFreez717