    Question Higher efficiency ac



    Ever wonder what makes a 13 seer different from a 10 seer? I have-and what I've seen from my experience is a difference in the surface area of the coils. I saw a 10 seer Carrier side by side with a 13, used the same compressor, but the condenser was physically larger. Is that all it amounts to? If so, what are the limitations of compressor-to-condenser sizes, i.e., could you use a 3 ton compressor in a 5 ton condenser (for a 3 ton load), and expect a higher efficiency?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Higher efficiency ac

    Yes, the bigger the condenser, the higher efficiency expected, provivided SC is within manufacturer spec.

  3. #3
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Higher efficiency ac

    Quote Originally Posted by Stoofer
    Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?
    Yes and no the larger condenser would be good and the lower speed of the compressor should be more effecient, but that would depend on the compressor selection

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Higher efficiency ac

    Quote Originally Posted by Stoofer
    Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?
    You can't "only run one of the indoor units" on a twin split. You can on a multi system.

  6. #6
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    Sorry was meaning Multi split I've been looking at a few sysytems with the view of heating/cooling my conservatory and living room, anyone got views on these systems Mitsubishi SCM45ZD Vaillant V6-060 M2N and I belive Tosh now do a Daiseikai 2 though this maybe beyond my buget.

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Higher efficiency ac

    Quote Originally Posted by Stoofer
    Sorry was meaning Multi split I've been looking at a few sysytems with the view of heating/cooling my conservatory and living room, anyone got views on these systems Mitsubishi SCM45ZD Vaillant V6-060 M2N and I belive Tosh now do a Daiseikai 2 though this maybe beyond my buget.
    The Daiseikai is the most effecient on the market at the moment The RAS 10 has a COP of 4.51

    Shop about this is a domestic product and as such should be affordable, try another supplier

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  8. #8
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    Cheers for the advice Andy that COP really appeals to a double tight Bas***d like me

  9. #9
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Higher efficiency ac

    Quote Originally Posted by Stoofer
    Cheers for the advice Andy that COP really appeals to a double tight Bas***d like me
    No prob

    just to note that COP is mid range, these units about 2.5kW in this case. Range is 0.5 to 3.5kW.

    Try and select your unit at required duty in this sweet spot

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  10. #10
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    Sorry to be a bit dense Andy , are you saying if my room requires 2.5kw of duty fit a 3.5kw unit and it will run more effiecently in it's mid range?

    I should have the signature "If it's too hard i can't understand it"

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Higher efficiency ac

    I don't know if Andy meant this but selecting a larger indoor unit is mostly a good solution.

    In a non-inverter situation, unit will evaporate higher, so COP will increase.

    With an inverter, heatload can be 'absorbed' at a lower speed, so reducing noise. At partial load, compressor will run sooner on a lower speed increasing it's COP.

    Also less wearing on the compressor bearings.

    When I started many yeras ago, when we installed a Daikin, we allways ordered a bigger indoor size then the outdoor unit.

    When is it not a good solution? For those who lives in very humid climates and need to dehumidificate a lot.
    Last edited by Peter_1; 23-07-2006 at 09:46 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    Cheer's for the explanation Pete, I'm gonna take Andy’s advice and shop around for a Daiseikai 2 to supply my living room and conservatory, the room unit will get much more use so I'll go for next size up now as dehumidifying isn't really necessary for me.

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Higher efficiency ac

    Quote Originally Posted by Stoofer
    Cheer's for the explanation Pete, I'm gonna take Andy’s advice and shop around for a Daiseikai 2 to supply my living room and conservatory, the room unit will get much more use so I'll go for next size up now as dehumidifying isn't really necessary for me.
    With inverter units the book value at the greatest COP is the one to go for.

    If your room needs 2.5kw a 2.5kW nominal inverter is the one to go for, it already has the over sized indoor, a the 2.5kW will do 3.5kW maximum

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    Join Date
    Oct 2004
    Location
    UK
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Higher efficiency ac

    ok cheers for info guys.

  15. #15
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Higher efficiency ac

    When is it not a good solution, for those who lives in very humid climates and need to dehumidificate a lot.
    Use a two speed indoor fan and switch it to low when the humidity is high.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

Similar Threads

  1. Replies: 5
    Last Post: 24-07-2006, 03:28 PM
  2. New idea for higher efficiency
    By star882 in forum New Technologies
    Replies: 7
    Last Post: 22-02-2006, 04:22 PM
  3. AKV versus higher load
    By Peter_1 in forum Industrial
    Replies: 20
    Last Post: 18-04-2004, 11:05 AM
  4. Compressor's volume efficiency
    By John McGru in forum Fundamentals
    Replies: 0
    Last Post: 16-02-2004, 08:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •