Results 1 to 11 of 11
-
09-07-2006, 08:07 PM #1
Is a capillary tube considered to be a modulating mtering device, as a TXV is.
<i>Sorry for the double post, please remove th eother if it is a problem.</i>
I have often pondered this query, and have found many different answers to it
What do you think it is?
modulating metering device or not ?
I have oftened wondered this because the tube responds to subcooling unlike a fixed oriface would, and more like a TXV does.
-
19-07-2006, 06:44 PM #2
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
I always thought cap tube and fixed were the same....this is what I found;
Fixed ( non-moving ) metering devices, such as capillary tubes, orifices, etc., never adjust to system conditions, therfor standard fluid dynamics come into play, where a higher pressure pushing in ( head pressure ), in relation to a lower resisting pressure on the other side ( back or evaporator pressure ) means more ***** flow. Lower head pressures mean less flow. Thus, there is no active control of superheat. If you were to charge a system of this type 'to a full glass' under most conditions, you would be incorrectly charged ( generally overcharged, but actually undercharged in some cold weather conditions ). Thus, having a sight glass would be misleading, as it would be telling you a fact that is not relevent to correct charge.
-
19-07-2006, 11:08 PM #3
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Originally Posted by TopMechanic
-
19-07-2006, 11:35 PM #4
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
I think the key term here is "modulating". Cap tubes, orifices, & TXV's are all metering devices.
With orifices or cap tubes you get what you get depending on charge and the info wambat provided.
The TXV's however will modulate to control superheat.
To do that with a cap tube or orifice you would have to continually vary the refrigerant charge right?
That makes the cap tubes and orifices non-modulating the way I see it.
-
20-07-2006, 05:06 AM #5
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Originally Posted by US Iceman
(v) change the key of, in music; "modulate the melody"
(v) of one''s speech, varying the pitch
(v) fix or adjust the time, amount, degree, or rate of; "regulate the temperature"; "modulate the pitch"
(v) adjust the pitch, tone, or volume of
(v) vary the frequency, amplitude, phase, or other characteristic of (electromagnetic waves)
-
20-07-2006, 11:19 AM #6
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
I guess one could say that a TXV is temperature modulating (hence the word thermostatic) and cap tube is pressure modulating. PRV (Pressure Regulated Valve) ???
-
20-07-2006, 03:20 PM #7
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
OK, so we're both right.
My thoughts were the TXV is capable of adjusting to various operating conditions. In other words it has some means of self-control as a response to a change, i.e., independent control.
On the other hand, the cap tube is dependent on a change in the operating conditions to cause a variation in flow.
Of course the question was not which one is dependent or independent of system changes. So I think there is where is I'll stop.
-
20-07-2006, 08:54 PM #8
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Regarding capilary metered systems, do you consider that is efective to control the compressor speed to adjust the cooling capacity (ie with an inverter)?
-
20-07-2006, 09:37 PM #9
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Originally Posted by davidk
-
20-07-2006, 09:39 PM #10
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Originally Posted by US Iceman
-
20-07-2006, 10:00 PM #11
Re: Is a capillary tube considered to be a modulating mtering device, as a TXV is.
Don't go all squishy on me. I still have a reputation to protect.
Aren't discussions more fun when their civil?
Similar Threads
-
Capillary tube prices in the UK
By trial in forum FundamentalsReplies: 4Last Post: 18-09-2007, 12:16 PM -
Is a capillary tube considered to be a modulating mtering device, as a TXV is.
By TopMechanic in forum Technical DiscussionsReplies: 2Last Post: 20-08-2006, 07:51 PM -
:rolleyes: capillary tube size in distributor?
By abbasi in forum New TechnologiesReplies: 2Last Post: 08-07-2006, 03:56 PM -
metric capillary tube
By tralex in forum FundamentalsReplies: 5Last Post: 21-02-2006, 06:57 AM