    Climaveneta ERACS-Q/B 152



    Good Day, I have an AL:131 Anomaly Compressor No.1 on this unit and have failed to reset it and to find out what is causing the Alarm and where its coming from. Could you assist with info or literature on this Alarm. Also I wanted to find out how the condensor fans are controlled as they are two speed but cannot change direction on the one fan on Compressor No.2. It keeps going the wrong way no matter if you reverse the phases.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Climaveneta ERACS-Q/B 152

    Can't help with the compressor problem but with the fans, you will find that the one going backwards is not powered but moving due the the airflow from the first one.
    The condenser fans are normally staged based on discharge pressure.

  3. #3
    Join Date
    Sep 2009
    Location
    Harare, Zimbabwe
    Posts
    11
    Rep Power
    0

    Re: Climaveneta ERACS-Q/B 152

    Quote Originally Posted by frank View Post
    Can't help with the compressor problem but with the fans, you will find that the one going backwards is not powered but moving due the the airflow from the first one.
    The condenser fans are normally staged based on discharge pressure.
    The unit starts one then the compressor kicks in and you find that the one that starts is going the correct direction, the it kicks in the other two and they go the wrong way ??

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Climaveneta ERACS-Q/B 152

    Hi Freddy.
    just to confirm what you already state. when i check against the alarm codes i have for a different model to yours listed. It say's Motor of compressor (1,2,3 or 4) overheated or any fault.
    Some diagnostic checks on your system are needed.
    Just humour me, try disconnecting the suspect fan electrically ( pulling fuses is usually the favorite!) and run the system. Because as Frank rightly says on a multi fan system. it is quite common to see adjacent fans spinning in the opposite direction albeit slower! Provided you have a wiring system, it should be relatively easy to identify where the fault is.
    Good luck grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Climaveneta ERACS-Q/B 152

    Just a thought Freddy. Check your Fan Phase fuses!