    Arrow Operation theater



    What is the experience of using VRF outdoor unit with DX AHU for air conditioning an operation theater. Is there any reason that dictated this combination as inferior to that of Air Cooled Chiller with Chilled water AHU.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Operation theater

    Can you go low enough for - I guess - surgical operating room?
    If so, will filtering on a standard VRF unit sufficient?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jun 2023
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Operation theater

    Depends on what you're trying to do?? it'd be ok for around the theatre to maintain the temperature but not ideal for air introduced at or around the operating table itself. I highly recommend researching the applicable codes for this as pressure gradients from theatre to prep room may be required and a close control temperature/rh band and specific air quality (airborne particulates) may be required for introducing air into the theatre

    Some may require as many as 20 ac/h and have an anti bacterial/viral capability,
    Last edited by TrevH; 11-12-2023 at 02:48 AM.