    Thumbs up Cold Storage Unit Selection



    Dear Forum,
    I feel some body will help me .I m working in Middle east where the ambient goes upto 50 Deg C and falls down to 15 Deg C , Due to the high difference in ambient it is very difficult to size an evapourator(Due to the huge diff in Ref KW because of heavy different in ambient)
    I need someons help in sizing



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Cold Storage Unit Selection

    and Size the condencer for the 50+C Ambient then use a VFD type fan to make up for the temp swing.

  3. #3
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Cold Storage Unit Selection

    make sure in your calcs that youinclude the correct insulation, product load,operatives,lighting,any other heat source ie fork trucks etc and very important,doors and how many entry-exits, equipement as above,remote condenser with fan speed control.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Storage Unit Selection

    Quote Originally Posted by The MG Pony
    and Size the condencer for the 50+C Ambient then use a VFD type fan to make up for the temp swing.
    Yeah, but in low ambient temp, vfd will slow the compressor down, eventually the evaporator will dry out, superheating will shoot in sky, and compressor will overheat. Apart from that, you can only make use of electronic XV for working on that large range of conditions.
    If you are working with a dx evaporator for cooling air directly, than you probably be better install multiple evaporators and multiple circuits, so that each of them will work approx in the same conditions.
    In low ambient, switch off one or more of the circuits.

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Cold Storage Unit Selection

    No that cool temp it shuts the fan off using the gas to keep a stable flow and when the ambiant goes to the point pur convection will not work the fan kicks in.

  6. #6
    Join Date
    May 2003
    Location
    India
    Age
    55
    Posts
    5
    Rep Power
    0

    Re: Cold Storage Unit Selection

    any body can give some idea about evapourator pressure regulator and will it solve this problem

  7. #7
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Cold Storage Unit Selection

    thought it was a DX system, whats all that about a variable speed fan being no good,if it ,s sensing the condensing temperature and running at a speed to maintaine it ,whats the problem ! or have i missunderstood.

  8. #8
    Join Date
    Jun 2006
    Location
    china
    Age
    45
    Posts
    14
    Rep Power
    0

    Re: Cold Storage Unit Selection

    Quote Originally Posted by NoNickName
    Yeah, but in low ambient temp, vfd will slow the compressor down, eventually the evaporator will dry out, superheating will shoot in sky, and compressor will overheat. Apart from that, you can only make use of electronic XV for working on that large range of conditions.
    If you are working with a dx evaporator for cooling air directly, than you probably be better install multiple evaporators and multiple circuits, so that each of them will work approx in the same conditions.
    In low ambient, switch off one or more of the circuits.
    I agree on the above, Especially required mutil-low hp-compressors on a rack. You can calculate the minmum heat load and max heat load, then select some small evaporators based on partly minmum heat load. When in minmum condition, there will be also a few small evaporators and small hp compressors for running to avoiding frequently on-off.

  9. #9
    Join Date
    Apr 2005
    Location
    Adelaide
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Cold Storage Unit Selection

    Hi Seej

    You have to select the evaporator for the maxium load during peak conditions otherwise yuor rooms will only work during the night, the trick here is not on the evaporator selection but on compressor selection & suction line sizing to handle the low load conditions. As for the condeser selction old gas bottle is right you just VF drive the fans

    Cheers

    Julian

  10. #10
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Cold Storage Unit Selection

    This may sound ludicrous.........but how about two systems, one to handle day loads, a smaller one to kick in at dusk.

  11. #11
    Join Date
    Jul 2006
    Location
    Israel
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Cold Storage Unit Selection

    Here we do it very simple , A) oversize condensing coil , B) a high pressure presostat without reset ( auto) to kick the condensing fan on , based on pressure , if a bigger system a couple of fans , then only one on by presostat.
    All the best , Tzvi.

  12. #12
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Cold Storage Unit Selection

    I regard the selection of compressor is also important, the T3 reciprocating compressor is the best choice. The temperature fluctuating in Mid East is tremendous, Using VFD condenser which controled by high pressure/ambient temp. may be better.

Similar Threads

  1. Cold storage - Onions room
    By Kevin Yeo in forum Fundamentals
    Replies: 31
    Last Post: 14-02-2008, 03:42 PM
  2. Cold Storage Calculations
    By HAROON in forum Fundamentals
    Replies: 7
    Last Post: 29-03-2007, 10:13 AM
  3. RH in potato cold storage
    By kryoboss in forum New Technologies
    Replies: 3
    Last Post: 18-08-2006, 02:18 PM
  4. Cold Storage Design
    By abbasi in forum Technical Discussions
    Replies: 11
    Last Post: 06-01-2005, 07:17 PM
  5. cold storage pictures
    By stan1488 in forum Industrial
    Replies: 2
    Last Post: 29-09-2004, 04:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •