09-07-2006, 04:55 PM #1
Cold Storage Unit Selection
Dear Forum,
I feel some body will help me .I m working in Middle east where the ambient goes upto 50 Deg C and falls down to 15 Deg C , Due to the high difference in ambient it is very difficult to size an evapourator(Due to the huge diff in Ref KW because of heavy different in ambient)
I need someons help in sizing
-
09-07-2006, 08:40 PM #2
Re: Cold Storage Unit Selection
and Size the condencer for the 50+C Ambient then use a VFD type fan to make up for the temp swing.
-
10-07-2006, 07:49 AM #3
Re: Cold Storage Unit Selection
make sure in your calcs that youinclude the correct insulation, product load,operatives,lighting,any other heat source ie fork trucks etc and very important,doors and how many entry-exits, equipement as above,remote condenser with fan speed control.
-
10-07-2006, 09:11 AM #4
Re: Cold Storage Unit Selection
Originally Posted by The MG Pony
If you are working with a dx evaporator for cooling air directly, than you probably be better install multiple evaporators and multiple circuits, so that each of them will work approx in the same conditions.
In low ambient, switch off one or more of the circuits.
-
10-07-2006, 09:50 AM #5
Re: Cold Storage Unit Selection
No that cool temp it shuts the fan off using the gas to keep a stable flow and when the ambiant goes to the point pur convection will not work the fan kicks in.
-
10-07-2006, 10:32 AM #6
Re: Cold Storage Unit Selection
any body can give some idea about evapourator pressure regulator and will it solve this problem
-
10-07-2006, 03:24 PM #7
Re: Cold Storage Unit Selection
thought it was a DX system, whats all that about a variable speed fan being no good,if it ,s sensing the condensing temperature and running at a speed to maintaine it ,whats the problem ! or have i missunderstood.
-
10-07-2006, 05:07 PM #8
Re: Cold Storage Unit Selection
Originally Posted by NoNickName
-
11-07-2006, 05:35 AM #9
Re: Cold Storage Unit Selection
Hi Seej
You have to select the evaporator for the maxium load during peak conditions otherwise yuor rooms will only work during the night, the trick here is not on the evaporator selection but on compressor selection & suction line sizing to handle the low load conditions. As for the condeser selction old gas bottle is right you just VF drive the fans
Cheers
Julian
-
11-07-2006, 02:37 PM #10
Re: Cold Storage Unit Selection
This may sound ludicrous.........but how about two systems, one to handle day loads, a smaller one to kick in at dusk.
-
11-07-2006, 04:30 PM #11
Re: Cold Storage Unit Selection
Here we do it very simple , A) oversize condensing coil , B) a high pressure presostat without reset ( auto) to kick the condensing fan on , based on pressure , if a bigger system a couple of fans , then only one on by presostat.
All the best , Tzvi.
-
20-07-2006, 09:28 AM #12
Re: Cold Storage Unit Selection
I regard the selection of compressor is also important, the T3 reciprocating compressor is the best choice. The temperature fluctuating in Mid East is tremendous, Using VFD condenser which controled by high pressure/ambient temp. may be better.
Similar Threads
-
Cold storage - Onions room
By Kevin Yeo in forum FundamentalsReplies: 31Last Post: 14-02-2008, 03:42 PM -
Cold Storage Calculations
By HAROON in forum FundamentalsReplies: 7Last Post: 29-03-2007, 10:13 AM -
RH in potato cold storage
By kryoboss in forum New TechnologiesReplies: 3Last Post: 18-08-2006, 02:18 PM -
Cold Storage Design
By abbasi in forum Technical DiscussionsReplies: 11Last Post: 06-01-2005, 07:17 PM -
cold storage pictures
By stan1488 in forum IndustrialReplies: 2Last Post: 29-09-2004, 04:07 PM