Thread: water chiller
    Jun 2009
    saudia arabian
    28
    water chiller
    We have water chiller; it reduces water mix glycol temperature to 2-degree centigrade. But when it run all evaporators found ice in the refrigeration side (From expansion valve to suction of compressor line. *****, we use 404A. We use Copland compressor (scroll type). So, I want to know how can i remove ice formation in the evaporator.
    Feb 2011
    scotland
    458
    Re: water chiller
    If the ice is on the outside of the refrigerant pipework, maybe the insulation needs replacing.
    If the ice is inside the refrigerant pipes, you would need find out how the water got into the system.
    If the glycol inside the evaporator is freezing, the water/glycol mix concentration would be one of the things to check.
    Jun 2009
    saudia arabian
    28
    Re: water chiller
    thanks you your reply. now chiller is working goog. only issue is freezing inside evaporator coil.add gycol system is working good.