    water chiller



    We have water chiller; it reduces water mix glycol temperature to 2-degree centigrade. But when it run all evaporators found ice in the refrigeration side (From expansion valve to suction of compressor line. *****, we use 404A. We use Copland compressor (scroll type). So, I want to know how can i remove ice formation in the evaporator.



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: water chiller

    If the ice is on the outside of the refrigerant pipework, maybe the insulation needs replacing.

    If the ice is inside the refrigerant pipes, you would need find out how the water got into the system.

    If the glycol inside the evaporator is freezing, the water/glycol mix concentration would be one of the things to check.
    Last edited by seanf; 28-09-2023 at 01:05 PM.

  3. #3
    Join Date
    Jun 2009
    Location
    saudia arabian
    Age
    53
    Posts
    28
    Rep Power
    0

    Re: water chiller

    thanks you your reply. now chiller is working goog. only issue is freezing inside evaporator coil.add gycol system is working good.