    Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider



    Guys we need help

    We have relocated x2 LUVATA - CAP0251P condenser units (fan & coil) roughly 1m from their original location. The refrigerant gas is R410A. The condensers are connected to
    UNIFLAIR SUAC0151B. We have recovered the gas from the outdoor units, carried out the works, pressure tested, vacced out then charged with new R410a. When turning the units on we are getting a fault code - Low Evaporating Pressure on both systems. We haven't carried out any internal works but the fault keeps coming back after 5mins of running. Should we of replaced the filter driers? 6kg was pulled out so we charged with the same - pipe work is 1/2 5/8 roughly 45m.

    We mainly work on AC - Vrfs Vrvs Splits



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Did the systems work ok before you moved the condensers?

    Could be a bit undercharged now as it will take a fair bit of gas just to bring the system up to 0psi from a vacuum, plus the extra pipe.

    Are they critically charged systems or do they have a receiver and sight glass?

    Drier could be blocked, but odd to have two at the same time, if a drier is blocked you will get a temperature difference across it with the outlet being cooler, sometimes to the point of sweating or even ice forming on the pipe.

    Has anything else been turned off whilst the work was carried out and possibly forgotten about? Evap fan motor not running, belts loose/broken, poor air flow for other reasons, dampers shut in ductwork etc
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Do the pressures on your gauges show it dropping?
    Could the compressor oil have been washed out when recharging the units?
    Pipe cap/armaflex/stones in the new bit of pipe?

  4. #4
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Driers should have been changed.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Go back to basics and measure superheat, as well as looking at pressures.

  6. #6
    Join Date
    Sep 2023
    Location
    Romania
    Posts
    2
    Rep Power
    0

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Hello Frank, how can I post on the forum, I created an account today and I can't post. Thank you!

    PS: I succeeded.
    Last edited by Adrian; 24-09-2023 at 07:25 PM.

  7. #7
    Join Date
    Sep 2023
    Location
    UK
    Posts
    3
    Rep Power
    0

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Hi Monkey Spanners, thanks for your reply. Systems did work before we got our hands on them although we didn't check the error history. Sight glass is flashing slightly. all fans are running, we did notice the compressor was hot to touch on the top & very cold on the bottom

  8. #8
    Join Date
    Sep 2023
    Location
    UK
    Posts
    3
    Rep Power
    0

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Hi Seanf
    Pressures show the normal 120psi for R410a, Oil might be a factor, no stones or anything in the pipe work.

  9. #9
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Low Evap Pressure Fridge System HELP!!! - UNIFLAIR - Schneider

    Quote Originally Posted by FRMSAC View Post
    Hi Seanf
    Pressures show the normal 120psi for R410a, Oil might be a factor, no stones or anything in the pipe work.
    Does the pressure actually go down to the low pressure fault setting on the switch/controller?