    If the box was freezing inside, (shelves were developing ice as he said) yet the system never shut off.... (even when he manually shut the t-stat off)... I would say the t-stat contacts were arc'd closed. That could be from running too many appliances off the same circuit providing they called at the same time etc.

    I don't believe that I would go any deeper "knowing" the t-stat failed to shut the system down when he turned it off, or at least not yet. The ice on the shelves does suggest his door seals are leaking also. JMHO...

    By the way... I do agree with your thought on the frozen suction line though... frost on a suction line doesn't necessarily mean anything, depending on box temperature, ambient temperature and humidity level as you said.
    Last edited by subzero*psia; 13-01-2002 at 08:48 PM.
    :D
    Dean
    Subzero*psia

    Extinction is simply proof of failure to adapt.

Similar Threads

  1. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  2. One Half of a Part Wound Compressor Motor is Burnt
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 25-08-2003, 11:11 AM
  3. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM
  4. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •