    Mitsubishi electric city multi issues



    I’ve been asked to go look at something for a friend who has had a couple of people look at the system and had no joy in working out the fault and wanted some things to look at and opinions before I head over Thursday.

    Basicaly it’s a PUMY-p140VKM5 condenser and has 4 indoor units not sure on indoor unit kw but been told it’s 20 meters to furthest indoor and a total of 32 meters liquid pipe additional charge of 3.2 kg 410A making a total charge of 8kg.

    Basicaly it’s about 6-7 months old the install and was working fine over winter and In summer when they peope have used it for cooling after 3-4 hours it brings up a 1102 fault code (high discharge temp) the other people have weighed gas out and it’s the same 8kg as original installation. Tested it changed the discharge thermistor and stil happening after 3-4 hours running now in my opinion if it was a pcb it would fault instantly/ pretty quick not after 3-4 hours. I’ve been told the air offs of all 4 units in both heating and cooling are really good as well.

    So yeah any suggestions would be appreciated thank you.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi electric city multi issues

    Had similar on a Daikin vrv.
    Turned out to be an oil return problem.
    When system is cool, runs for a while and as compressor starts to heat up, lack of lubrication causes the compressor to overheat resulting in high discharge temp.

    On my system, turned out to be pipework installed over design max distance and the oil was collecting in the fan coils at the furthest point. Due to the excessive pipe lengths, the gas velocities at this extreme length were insufficient to carry the oil back to the compressor

  3. #3
    Join Date
    Aug 2023
    Location
    England
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi electric city multi issues

    Quote Originally Posted by frank View Post
    Had similar on a Daikin vrv.
    Turned out to be an oil return problem.
    When system is cool, runs for a while and as compressor starts to heat up, lack of lubrication causes the compressor to overheat resulting in high discharge temp.

    On my system, turned out to be pipework installed over design max distance and the oil was collecting in the fan coils at the furthest point. Due to the excessive pipe lengths, the gas velocities at this extreme length were insufficient to carry the oil back to the compressor

    I’m going to just go from scratch measure liquid line and sizes and indoor units use the calculator to bring up charge correct that if it’s wrong check running pressures condensing temps and another one that I’ve had cause it is the lev inside bc box not operating properly causing a lack of refrigerant back through the suction preventing compressor cooling if all else fails will ring tech 😂

  4. #4
    Join Date
    Aug 2023
    Location
    England
    Posts
    4
    Rep Power
    0

    Re: Mitsubishi electric city multi issues

    The max allowable pipe length for this condenser is massive so shouldn’t be that issue

  5. #5
    Join Date
    May 2010
    Location
    japan
    Posts
    19
    Rep Power
    0

    Re: Mitsubishi electric city multi issues

    It is most likely a defect in the discharge thermistor itself.
    Discharge thermistors have normal resistance values at room temperature, but shift sharply at high temperatures.

  6. #6
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Mitsubishi electric city multi issues

    have you checked the addressing and that the port connections on the BC box are piped and addressed correctly

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Mitsubishi electric city multi issues

    it the ports are piped incorrect or address incorrectly as units shut down on temp system might run on low pressure causing compressor to over heat