    City Multi Change temp sensor position on PEFY-P100VMHS-E



    Guys need to change return air sensor position from factory default position to wall control
    Being city multi it needs to be done by dip setting at the fcu.
    Can we confirm dip Sw1 No.1 to on?



  2. #2
    Join Date
    Sep 2023
    Location
    United States
    Posts
    1
    Rep Power
    0

    Re: City Multi Change temp sensor position on PEFY-P100VMHS-E

    Quote Originally Posted by Mavricks Choice View Post
    Guys need to change return air sensor position from factory default position to wall control
    Being city multi it needs to be bloxd io done by dip setting at the fcu.
    Can we confirm dip Sw1 No.1 to on?
    The static pressure setting is adjustable by changing a dip switch. The default setting is 0" W G, with options for 0.12" and 0.24" W G.

  3. #3
    Join Date
    Sep 2023
    Location
    Minto
    Posts
    1
    Rep Power
    0

    Re: City Multi Change temp sensor position on PEFY-P100VMHS-E

    Quote Originally Posted by Mavricks Choice View Post
    Guys need to change return air sensor position from factory default position to wall control
    Being city multi it needs to be done by dip setting at the fcu. fnaf security breach
    Can we confirm dip Sw1 No.1 to on?
    The SW banks should still match up, SW1 listed on the sticker is the correct bank but the dip switch number could be incorrect.