    Daikin Madoka



    Hi everybody,

    I’ve fitted a KRP2A adapter card to 2 systems each with an individual Madoka controller,
    However I can no longer set schedules on the Madoka app. I’m assuming the 2A is the causing the issue as I know it acts like a central controller on the D3 network . Any ideas? I’m using the 2A for fire shut down .

    Cheers



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Madoka

    What indoor fancoil model.
    Krp2a for vrv, VAM
    KRP4A for Skyair

  3. #3
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin Madoka

    All VRV frank �� 2A works off F1 / F2 while 4A works off P1/P2 .

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Madoka

    Yes, quite aware of that.
    Have you tried disconnecting the krp and then setting schedules to isolate the problem?

  5. #5
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin Madoka

    Hi Frank,

    The Daikin tech suggested that but the store was opening up yesterday so I couldn’t try it . I’ll let you know .

  6. #6
    Join Date
    Jan 2005
    Location
    Ireland
    Age
    43
    Posts
    111
    Rep Power
    21

    Re: Daikin Madoka

    What do you think of this Frank ?

    Field setting 1e - 4
    Schedule and Auto-changeover enabled when multizone controller is detected
    (Note 1)
    Native remote controller Schedule and Auto-changeover functions are disabled when a multizone controller is detected and a group address is assigned


    I thought i had gone through all the field settings but obviously didn’t read this correctly.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Madoka

    I'm thinking that it is the settings on the krp2a that is the issue. As you have now said that the krp is fitted to enable fire shut down (assuming B1 BC wiring to fire system), the blue dial setting needs to be set to allow input from the madoka.