    FNISHED! Recharge 410 and TXV Repair ( " they" said it couldnt be done)



    Trane XL14C 3 Ton package

    Recharge R410A

    *CHARGED VAPOUR

    *WITH COMPRESSOR OFF

    *Repaired broken TXV Thermostat bulb

    * Recharged bulb with 410 vapour

    *NO SEALED SYSTEM WORK TO FIX THE TXV

    Works perfectly:

    https://m.youtube.com/watch?v=H8s6NkkvMLg

    135 psi low side, +/- a little, depending on entering air conditions.

    170 psi R410 on the TXV bulb
    hi 80F outdoor
    mid 70F indoor
    50% RH
    nominal about 11.7 amp total package current,
    Cycle time at 74F indoor, 950 S.F. two level, with airflow problems, 10 minutes


    Interesting to note the main function of the thermostatic assembly is to shut the TXV at compressor off, obviously to preserve the liquid line contents.

    The diaphragm pressure at the bulb only affects the low side pressure up to a point.

    That is the stated low side pressure by the P&T cycle data from Trane. Increasing bulb presure past the point of stated low side pressure has little or no effect. The system pressures are controlled by indoor and outdoor temp and RH factors, not TXV operation.

    This TXV only has a control movement of 0.020 inch, so it appears to be more of an Off- On than a flow regulator.

    The info I received from this and other Internet forums was UNIVERSALLY WRONG.

    Info from Sporlan Tech was WRONG.

    Engineering, thermodynamics and chemistry knowlege told me to ignore it.

    I was right.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: FNISHED! Recharge 410 and TXV Repair ( " they" said it couldnt be done)

    Well Done You!
    However if your posts are continually going to criticise any and everything that someone posts. I for one will not weep if you take further issue and refrain from contributing.
    I am sure your style of contribution would be more appreciated maybe on the american forum.
    We are all here to help one another.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: FNISHED! Recharge 410 and TXV Repair ( " they" said it couldnt be done)

    .

    Some Expansion valves have a critical charge that acts as a capacity control.

    The charge in the bulb is reduced to stop the valve opening fully. In startup conditions or
    during high load situations the valve can't fully open due to the restricted charge in the bulb.

    Just one point I noticed from your video. Did you connect the bulb to the evaporator outlet so it sensed the refrigerant temp of the outlet of the evap?

    The video did not make it clear but it looked like you left it swinging in the airflow??

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..