    Unhappy Difficulty fitting tubing on discharge port



    Hello everyone, noob here. It wasn't clear to me that the copper ends of the compressors used non-annealed copper, so when I started using the swaging tool on it to fit 5mm OD tubing on 4.95mm discharge port of my embraco compressor, I realized it was pretty hard so I stopped before being able to fit the pipe, however you can see that the end has become slightly larger. Now it's clear to me that I have to heat up to anneal the copper before using the swaging tool, but my question is, how do I know if I have damaged it? I will be using R290 so I am paranoid about everything and I just don't want to have the end splitting on me under the high pressure of the discharge port.

    4568934589523492.png



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Difficulty fitting tubing on discharge port

    2 ways to deal with it.
    1, swage your pipe out a little so that it fits snuggly, or
    2, just fill in the gap with cupro brazing rod when you braze the joint

  3. #3
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: Difficulty fitting tubing on discharge port

    Could you use heat to relieve any stress created when the pipe was swaged?

    It dosnt look like youve swaged it too much, so I'm guessing theres still a good wall thickness to the comps pipe and theres no cracks?

    When youve done all your brazing on the system, give it a strength and leak test with nitrogen?

  4. #4
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Difficulty fitting tubing on discharge port

    Quote Originally Posted by frank View Post
    2 ways to deal with it.
    1, swage your pipe out a little so that it fits snuggly, or
    2, just fill in the gap with cupro brazing rod when you braze the joint
    Thanks frank, I plan on using % silver rod for every joint in this project

  5. #5
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Difficulty fitting tubing on discharge port

    Quote Originally Posted by seanf View Post
    Could you use heat to relieve any stress created when the pipe was swaged?

    It dosnt look like youve swaged it too much, so I'm guessing theres still a good wall thickness to the comps pipe and theres no cracks?

    When youve done all your brazing on the system, give it a strength and leak test with nitrogen?
    Hi Sean, yes ofc I stopped why before I saw any crack and I also believe that heating to cherry red will help relieving evental internal stresses. I plan on charging to 225 psig with nitrogen which I believe is standard testing for R290 systems.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Difficulty fitting tubing on discharge port

    Silver solder will not fill any gaps/cracks. Personally, with your situation, I would use a brazing rod

  7. #7
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Difficulty fitting tubing on discharge port

    Sorry Frank maybe I'm unfamiliar with the correct term in english, but by silver solder I was referring to an actual brazing rod with 34% silver content and melting point at arount 700°C by the name of Castolin RX 8840 and it's a product used by HVAC professionals here in Italy.

  8. #8
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Difficulty fitting tubing on discharge port

    Oh I understand, I think you meant me saying the silver solder used for electric components, no I would never use that with pressurized gasses, let alone flamable gasses. I know some people on youtube have posted some work of them using even lead solder in hvac systems and they often seem to hold prtetty well but I want to sleep with peace of mind and I only use what professionals use

  9. #9
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Difficulty fitting tubing on discharge port

    Have swagged compressor stubs without issue, the heat from brazing will remove any stresses you are worried about.
    If you want to avoid swagging the pipe you can wrap some electrical tape round the pipe you want to connect to the compressor and clamp it in your flaring block, this will squash the pipe a bit smaller (may take a couple of goes with increasing amounts of tape) so it fits in the stub. Clean all the tape and any residual glue off of the pipe before brazing.
    Mostly found in Oxfordshire, UK :)

  10. #10
    Join Date
    Aug 2023
    Location
    London
    Posts
    1
    Rep Power
    0

    Re: Difficulty fitting tubing on discharge port

    If it were me, I would call a professional to do it.

  11. #11
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Difficulty fitting tubing on discharge port

    .

    Hello.

    Those small compressors are designed to be copper to copper brazed so the
    pipe out of the compressor has a copper coating for that purpose.

    If you heat it up too much to open the end up you could damage the copper coating and
    then prevent a good brazed joint.

    You are using brazing rod with a 30% silver content so just braze it as though it was
    a normal copper to copper and use flux.

    Heat up the pipe, swage it and then braze it immediately so it does not heat up and cool
    down too many times.

    Use your brazing rod with flux and it will give you a good gas tight joint.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  12. #12
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Difficulty fitting tubing on discharge port

    Quote Originally Posted by vhchicken View Post
    If it were me, I would call a professional to do it.
    Hello.

    That is good advice, most of us would never have thought of that

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  13. #13
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Difficulty fitting tubing on discharge port

    Someone sent me a set of 'Spin Swage' and 'Spin flare' tools from the USA but I guess they would be available in Italy. They work with a 18v battery drill and they're very good. They have several advantages to the older type flaring/swageing kit such as you don't need a clamp to hold the pipe and also they spin fast enough and make enough heat to anneal the pipe as they go. I thought they just a gimmick kind of tool when I first saw them but I've been surprised how much I've used them and how well they work. The only disadvantage I've found with them is that they can leave small filings / swarf in the pipe after use so you need to angle the pipe downwards before use or be prepared to manually clean the inside of the pipe if it's horizontal.

    https://www.youtube.com/watch?v=iFOTxT1qkLk