    Sightglass Dirt or Scale???
    Can people please share their experience or thoughts on what might be on the inside of this sightglass?
    This was taken when the unit was running, spots on sightglass are stationary.
    Regards Dale
  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46
    Re: Sightglass Dirt or Scale???
    Looks like ****ty oil, whats the history on the system? See this sort of thing on systems that used to run mineral oil that now run HFC refrigerants and POE oil where not all the old oil has been cleaned out of the system.
    Mostly found in Oxfordshire, UK :)
  3. #3
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19
    Seems sludge formed in the system flushed into the sight glass. Also ensure the indicator paper is not burnt during brazing by use of correct flame direction and wet cloth.