    Measuring refrigerant flow with a Coriolis flowmeter



    Hello everyone, Always taking on something I know little about.

    We are purchasing a Coriolis flowmeter to more accurately determine the btuh requirement of our supermarket cases. My question is do any of you have experience with doing this?

    Thanks , Kengineering



  2. #2
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    223
    Rep Power
    19

    Re: Measuring refrigerant flow with a Coriolis flowmeter

    Hello,
    we currently use Hendress Hauser Coriolis mass flow meters.
    Our typical application is mass flow between MP and LP vessels on industrial ammonia systems.
    coriolis.jpg

    flowmeter must stay below the level in the MP vessel to avoid gas in the pipe.
    it must be supported to avoid vibrations and movements.

    the difficult is that with a non subcooled liquid you get bubbles and can loose the signal as well as with an ultrasonic flow meter.
    some off our systems are fitted with ultrasonic flow meters F721 and it works as well.
    https://www.flexim.com/us/product/fluxus-f721