Results 1 to 9 of 9
  1. #1
    Join Date
    Mar 2023
    Location
    England
    Posts
    7
    Rep Power
    0

    Integral fridges high head



    Had a Williams 2 door prep fridge struggling to Maintain setpoint today, condenser coil is clean, fans all ok, charge seems good but we have high ambient temps in the kitchen often exceeding 35°c and more when the ovens are opened.

    Any ideas to improve the head pressures in these environments?

    What ambients can these fridges comfortably work in?

    Any input would be appreciated.



  2. #2
    Join Date
    Jun 2023
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Integral fridges high head

    They leaving the doors open or overstocking with high heat load produce?

    Other than that try and improve the efficiency of the condenser.....clear paths for airflow, fridge in best location for ventilation etc..... perhaps Williams do an upgraded fan to increase the condenser efficiency?

    I believe the industrial standard for max ambient is 40C but only Williams can tell you what it's really capable of
    Last edited by TrevH; 13-06-2023 at 08:33 PM.

  3. #3
    Join Date
    Mar 2023
    Location
    England
    Posts
    7
    Rep Power
    0

    Re: Integral fridges high head

    It’s located directly opposite the ovens and they’re in and out the fridge like a yo-yo!

    I have considered the upgraded fan to improve Efficiency, TBH it’s just too warm in there and there in and out far to frequently to maintain 4°c but trying to tell them that is like talking to a brick wall.

  4. #4
    Join Date
    Jun 2023
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Integral fridges high head

    I feel that pain,

    Tell them that if they don't address it then catastrophic failure is the most likely outcome for the fridge and it's contents. Tell them to up the air change rate for the kitchen with some DX LOL

  5. #5
    Join Date
    Mar 2023
    Location
    England
    Posts
    7
    Rep Power
    0

    Re: Integral fridges high head

    They laughed aswel when I mentioned additional cooling being installed ��!

  6. #6
    Join Date
    Jun 2023
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: Integral fridges high head

    Bless them LOL, at least they had a chance to laugh before the tears start

  7. #7
    Join Date
    Jun 2023
    Location
    usa
    Posts
    20
    Rep Power
    0

    Re: Integral fridges high head

    cool air supply for the condenser. It has nowhere to reject heat to.

    Or cool water...

  8. #8
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: Integral fridges high head

    The cheap option not just to move the fridges or the ovens elsewhere?

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Integral fridges high head

    I hope you're charging for each call out? If customer won't listen, i'd suggest dropping them, this problem is unfixable, max ambient used to be 32c for these and that was with the condenser at low level, all very well them laughing at your suggestions, what happens when health inspector calls and measures temps far above that allowed, issues a warning and then customer is on blaming you for not fixing it?
    Mostly found in the southern part of this green and pleasant land.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •