    Heat load and capillary tube



    Hey guys, I'm trying to calculate the capillary tube size for my project but I'm not sure I'm entering the correct data into the Secop tool because the recommended capillary size seems kinda off. Am I wrong assuming that I can treat the cooling capacity as heat load on this tool? The other data is correct because I need to aim for -35 C for the evaporator and +35 C for the condenser. Thank you!

    2345823534987.jpeg
    Attached Images Attached Images



  2. #2
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Heat load and capillary tube

    Yeah, Secop results don't look right

    Attached Images Attached Images

  3. #3
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Heat load and capillary tube

    Amazing, that's more like it!

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat load and capillary tube

    What I found more reliable for capillary tube reference is Embraco compressor handbook! Match your compressor displacement and working condition with that of Embraco and start from there! Sometime you need some length adjustment but most of the time you are good!

    Off course, heat load balancing between compressor, evaporator and condenser should be done before that!
    Last edited by nike123; 30-04-2023 at 03:49 PM.