    Cascade System Querry



    A cascade system with R-404A refrigerant on high side designed for -35 deg C evaporating and 45 deg C condensing temperature motor tripping on winding temperature thermistor. The suction gas temperature recorded at suction valve is (-18) deg C with the gage pressure of 0.8 bar ; a clear 18 deg C superheat. Could the high suction superheat contribute to tripping thermistor while the envelop is withi limit?
    OR ELSE WHAT COULD CONTRIBUTE TO MOTOR TRIPPING ?
    KORANNE



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Cascade System Querry

    High return gas temperature can cause the motors to heat up. Loose motor connections can also cause a higher than normal amp draw. Or insufficient motor cooling, i.e., no air flow on motor.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Cascade System Querry

    Quote Originally Posted by D.D.KORANNE
    A cascade system with R-404A refrigerant on high side designed for -35 deg C evaporating and 45 deg C condensing temperature motor tripping on winding temperature thermistor. The suction gas temperature recorded at suction valve is (-18) deg C with the gage pressure of 0.8 bar ; a clear 18 deg C superheat. Could the high suction superheat contribute to tripping thermistor while the envelop is withi limit?
    OR ELSE WHAT COULD CONTRIBUTE TO MOTOR TRIPPING ?
    KORANNE
    Faulty motor, winding problem

    Worn compressor (check discharge temperature)

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Cascade System Querry

    We last had a Bitzer (2 years old) which tripped on the internal thermistor (Kriwan).
    Measured the values at standstill and at room temperature and there was a largz deviation from normal.
    So, one of the thermistors is giving a false reading.
    But this can't be repaired, so it runs now only on the overload relay.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Cascade Refrigeration System
    By Vincent Yu in forum Fundamentals
    Replies: 71
    Last Post: 16-02-2012, 04:04 AM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  4. R-23 cascade system
    By S.M.Gokhale in forum Industrial
    Replies: 22
    Last Post: 08-08-2009, 08:04 AM
  5. problem in Auto Refrigeration Cascade System
    By ernestlin in forum Trouble Shooting
    Replies: 17
    Last Post: 01-07-2009, 12:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •