    Compressor for R290 rerigerant



    Hi there, sorry to bother again. I've just seen a video on YT of a guy dismanteling his broken AC unit to repurpose its condensing unit for a R290 project. I was wondering if there could be dangers in doing so, other than the fact that the fan on a class A3 refrigerant unit should not provide sparks or ignition sources, if the pressure levels are fine, can it be used safely? I mean, it's just a pipe of copper with fins, why would it be different from other refrigerants?



  2. #2
    Join Date
    Oct 2022
    Location
    Italia
    Posts
    49
    Rep Power
    0

    Re: Compressor for R290 rerigerant

    Ahhh damn, I was supposed to say "Condenser" in the title, not compressor. I know compressors are very specific on the type of refrigerant and should not be swapped.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Compressor for R290 rerigerant

    You can as you said use it for any refrigerant... mith the correct oil, compressor can run mostly on R290 as long as you do not overload the compressor motor ... a compressor is in fact just a simple gaspump
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Compressor for R290 rerigerant

    The copper condenser coil from an AC unit should be fine to use with R290. Just remember to leak check it, and maybe blow it through with nitrogen to try and get out any old oil.
    Last edited by seanf; 24-04-2023 at 09:55 PM.
    Interested to hear about opportunities to learn - linkedin.com/in/s34nf

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor for R290 rerigerant

    Anyone who does some work on A type refrigerants should consider what are liabilities connected with that!