    Hi all,
    I have been working on a Carrier Primeline reefer for the past two weeks, however, I am unable to solve the problem.
    Reefer model #69NT40-561-018
    The system has a restriction, and the compressor runs in a vacuum after the three-bump start.
    Controller alarm: AA28 - low suction pressure
    replace filter drier, replaced all transducers: EPT, SPT &DPT
    Replace EEV complete body and coil, replace DUV complete body and coil, replace evaporator temp sensor ETS1 and EST2
    The controller interchange (on problem with the controller)
    Thanks in advance,
    KRampersad
    Oct 2003
    5,630
    34
    Re: Technical difficulties
    Controller closes the EEV because you already replaced all other possible causes (but why if you were not certain about the real cause/problem?)?
    Seems very basic schematic...
    Feb 2011
    scotland
    456
    What does it do on the Pre-trip test?
    Did you blow through the pipework with nitrogen to check for any restrictions while you had components removed?