    Re: Condenser restriction

    Florian,
    Try running lower discharge pressure.
    Lower cut in & out, as 220 psi cut in 190 psi cut out, see what happens.
    Compressor probably has thermal overload to protect it.
    As previously suggested check or ideally change filter drier.

    Check amps if close to maximum, if okay let it run, add more refrigerant.
    82 deg F not to hot, condenser fan will work itself out then.
    Again check for more leaks.


    Note R404a has to be charges as a liquid, preferably into liquid line, not compressor suction.
    If you have had a few leaks & topped up, best change complete refrigerant charge.
    Last edited by RANGER1; 18-01-2023 at 10:26 AM.