    Sep 2022
    Canada
    3
    Ice Bank / Ice Thermal Storage
    Do you know how to calculate an ice bank with chilld glycol?
    Do you have any documentation, calculation sheet, software, drawings, etc.
    Do you know someone who could make the calculation for a fee. We are in Canada.
    Thank you,
    Feb 2011
    scotland
    458
    Re: Ice Bank / Ice Thermal Storage
    Could you get a rough idea by looking at the specific heat capacity of water and of ice, and the latent heat capacity of the phase change from ice to water. And then use this to work out the mass of ice or water youd need to give enough cooling capacity over the temperature range you want?
    Like,
    2kg of water cooled by 2K gives roughly, 4.2KJ/Kg.K X 2Kg X 2K = 16.8KJ
    2Kg of water going through the phase change gives roughly, 334 KJ X 2Kg = 668KJ
    2Kg of ice cooled by 2K gives roughly, 2.1KJ/Kg.K X 2Kg X 2K = 8.4KJ
    Total capacity = 693KJ
    Then you need to take into consideration heat transfer through the ice bank container, and any other heat sources.
    Theres probably free online calculators you can use.
    How important it is to get the correct cooling capacity for your project?
    Interested to hear about opportunities to learn - linkedin.com/in/s34nf
    Aug 2022
    United States
    28
    If you are looking at buying an ice builder, I believe you could get a manufacturer like Chester Jensen to provide that information as part of the sales process. https://www.chester-jensen.com/ice-builder
    What part of Canada are you in? I know some refrigeration engineers in Canada who might be interested in helping with this process.
    MrFreez717
Tags for this Thread