    water chillers



    Hi There,

    I was wondering if anyone out there could tell me if it matters which direction the water flows through tube type evap heat exchangers, or should it always go in at the liquid end and come out at the suction end or vice versa.

    Thanks

    Alex B



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: water chillers

    Hi Alex,

    In most cases it does not matter. The shell & tube exchangers are usually multiple pass meaning the water or refrigerant flows from one end to the opposite end and back multiple times.

    On most exchangers with an even number of passes, the liquid and suction are normally on one end for DX purposes.

    If the liquid is on one end and the suction is on the other, then I would suppose you have an exchanger with an odd number of passes: 1,3, etc.

    You can only confirm this by manufacturers technical data or by taking the head off, which of course requires new gaskets.

    Might I ask why you inquired about this?

  3. #3
    Join Date
    May 2006
    Location
    scotland
    Posts
    31
    Rep Power
    0

    Re: water chillers

    Hay Iceman,

    The reason I ask this is I am currenly working on a carrier 30gf system that was recently re piped and it keeps showing fualt code low chiller flow, i was wondering if the piped the water in the wrong direction and the water temp sensors are picking this up.

    Thanks
    alex

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: water chillers

    Hey Alex,

    Is the low flow fault being caused by a flow switch or flow sensing device? It might be a simple as the "flow switch" is not bi-directional.

    Or, the flow switch is opening on increase in flow, which would mean the switch is wired incorrectly.

    Or, as you say, the temp. sensors may be simply be sensing the temperatures in reverse, which could generate a fault.

    If either of these is true, then I guess you could say the chiller is pipe backwards.

    Has anyone checked the pumps to ensure they are running the correct direction and pumping full flow?

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: water chillers

    Alex,

    I found some information on a series 30HZ. Hopefully it is similar to yours.

    On page 6 the diagram shows the chiller water connections. Page 7 shows the symbol listing detailing the inlet & outlet.

    Product Data
    http://eto.carrier.com/litterature/p...sd_01_2003.pdf


    Operation & Installation Manual
    http://eto.carrier.com/litterature/iom/13412.pdf


    Wiring Diagrams
    http://eto.carrier.com/litterature/s...508667EE__.pdf


    Controls Manual
    http://eto.carrier.com/litterature/cm/13411.pdf

    Some of the files are under 1MB, while one is almost 2MB.

    I hope these are close enough to help you.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: water chillers

    Many manufacturers like us do not use flow switches, but differential pressure switches. That sort of pressure switch does only operate on positive pressure, that is if the pump is reversed, the chiller will stop.
    And yes, the evaporator, whether s&t or phe, does have a preferred water flow, that is counterflow to coldest refrigerant. Water condensers are 2 or 4 passes, but evaporators are very frequently single pass, so the direction of flow is fundamental.

  7. #7
    Join Date
    Jul 2006
    Location
    CN
    Age
    39
    Posts
    20
    Rep Power
    0

    Re: water chillers

    I just talk about the direction of water flow:

    Normally,the inlet of chilled water is near the refrigerant suction inlet of DX evaperator to increase the SUCTION super heat degree.otherside,the inlet of cooling water is near the outlet of condenser to increase liquid sub-cool degree.

  8. #8
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: water chillers

    Carrier 30GF flotronic 1 trips on flow problems if it senses the entering water temperature is dropping lower than the leaving temperature

Similar Threads

  1. Climaveneta water chillers
    By chillerman2006 in forum Industrial
    Replies: 28
    Last Post: 21-02-2011, 04:51 PM
  2. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  3. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 07:19 PM
  4. Carrier Water Chillers
    By Latte in forum Air Conditioning
    Replies: 10
    Last Post: 11-10-2008, 08:43 PM
  5. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •