    Fujitsu AC not running



    Hi can anybody help,

    We are looking at a Fujitsu AOY54RBA3L split with an underslung inside unit. I have the three phases to the outdoor unit and also the single phase to the indoor unit, the fan run's indoors but the control signal to the outdoor unit is only 120v is this right or should the signal be 240v.

    Any ideas as to why the compressor will not run

    Cheers



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fujitsu AC not running

    Any ideas as to why the compressor will not run
    Obviously something is interupting the control circuit.

    Are there any fault codes showing on the controller?

  3. #3
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Fujitsu AC not running

    I do have a fair idea why it does not run as this i right up my particular street of expertise, however due to certain recent redundancies i would not urinate on someone who calles himself/herself "TEAM" york if he/she were on fire.

    Do what i do, get a meter and figure it out yourself.
    Takes a licking, keeps on ticking.

  4. #4
    Join Date
    Apr 2006
    Location
    Libya
    Posts
    18
    Rep Power
    0

    Re: Fujitsu AC not running

    If you want to know the right voltage weather it is 120 or 240 v. then simply check the contactor voltage ,if it is 240 v the the signal must be 240 .IF you find that the voltage must be 240 and you have 120 first check the wiring to the indoor unit carefully specially the ground wiring,after all check the control board you will
    find may a relay controls the signal to the outdoor unit
    check it ,almost it runs by 12 V. DC if its voltage are correct then the possibilities are open .

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Fujitsu AC not running

    Quote Originally Posted by slingblade
    I do have a fair idea why it does not run as this i right up my particular street of expertise, however due to certain recent redundancies i would not urinate on someone who calles himself/herself "TEAM" york if he/she were on fire.

    Do what i do, get a meter and figure it out yourself.
    This is exactly my first thought when I read the post. A team should have at least one professional trouble shooter

  6. #6
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Fujitsu AC not running

    R407.c. 3 phase? 240v coil to contactor, installed many, never had this problem thou, NNNNNNNNNNNNeutral

  7. #7
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Fujitsu AC not running

    I believe that the Fujitsu control signal is always 120v at all times. Something to do with fuzzy logic.
    As for the comp not running then there may be a fault within the pcb. Good luck!

    Regards
    Jase

  8. #8
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: Fujitsu AC not running

    ouch, some bad feelings there eh.
    they that bad?

  9. #9
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: Fujitsu AC not running

    definately 240v signal for control circuit from indoor board

  10. #10
    Join Date
    May 2006
    Location
    Cheshire
    Posts
    9
    Rep Power
    0

    Re: Fujitsu AC not running

    Thanks for the help lad's I got it sorted in the end, dodgy discharge sensor.
    As for slingblade, it's Yorks policy to cut out tossers, any decent engineer would have been relocated or another company would have snapped you up. Redundancy is a part of life GET OVER IT!!

  11. #11
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Fujitsu AC not running

    Quote Originally Posted by Team York
    Thanks for the help lad's I got it sorted in the end, dodgy discharge sensor.
    As for slingblade, it's Yorks policy to cut out tossers, any decent engineer would have been relocated or another company would have snapped you up. Redundancy is a part of life GET OVER IT!!

    LMFAO.
    I have never nor will i ever work for York. It was not an engineering position i was refering to nor was it myself, and given it is Johnson controls who runs the show these days i would watch what you say. Tosser indeed, LOL.

    p.s. congratualtions on mending a split a/c unit, these can be very tricky indeed.
    Takes a licking, keeps on ticking.

Similar Threads

  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Replies: 18
    Last Post: 26-08-2009, 05:06 PM
  2. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Replies: 7
    Last Post: 04-08-2007, 09:06 PM
  3. fujitsu a/c running off generator
    By tait71 in forum Electrical
    Replies: 4
    Last Post: 17-07-2006, 08:25 PM
  4. fujitsu tech info
    By Krups in forum Air Conditioning
    Replies: 11
    Last Post: 01-12-2005, 07:41 PM
  5. Fujitsu AOT 24RZAL
    By Temprite in forum Air Conditioning
    Replies: 5
    Last Post: 31-10-2005, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •